    Nov 2014
    Bahrain
    11
    Coefficient of performance
    If the condensing temperature and evaporating temperature is constant but the power of the compressor ( driven by gas turbine ) changed . Can be assume that the coefficient of performance is constant ?
    May 2012
    54
    1,325
    30
    Re: Coefficient of performance
    No.
    The coefficient is a calculation of the energy imparted through the
    compression process divided into the energy absorbed or rejected
    through the heat exchanger.
    COP = RE/WD
    COP = THR/WD
    RE being refrigeration effect, heat absorbed by evap.
    THR being total heat rejected in cond.
    WD being work done in compression process.
    Rob
    Nov 2014
    Bahrain
    11
    No.
    COP = RE/WD
    COP = THR/WD
    Rob
    ok
    If coefficient of performane is 2 . It means the refrigerant removes 2 units of heat for each unit of energy consumed , right ?
    So If the work input is 1 kW the refrigeration effect is 2 kW
    Now , if the work input 2 kW , is the refrigeration effect will be 4 kW ??
    If that true , It means that the coefficient of performance is constant ????
    May 2012
    54
    1,325
    30
    Quote Originally Posted by chemicalENG View Post
    ok
    OK, sorry in that context "yes".
    COP is a ratio, nothing more so inputs and outputs can change but
    the ratio could remain constant.
    Rob