    Re: Variable Amperage And Cold Liquid line

    Discharge 225 psi
    Suction 45 psi
    Amperage between 35 - 50 ( copeland scroll / nominal 30 A)
    Unloaded: 13 A
    And the liquid line is cold specially after sight glass
    Last edited by hsn157134; 02-10-2014 at 09:50 AM.

  2. #2
    Join Date
    Feb 2014
    Location
    london
    Age
    38
    Posts
    24
    Rep Power
    0

    Re: Variable Amperage And Cold Liquid line

    Was your indoor unit running as heat pump or cooling?
    Have you checked compressor winding?
    After sight glass should be warm subcooled liquid. If its cold that could be a sign short of refrigerant. If you refer to PH chart you will know the compressor will always pull too many amps when its under charged.