    I have an A/c unit with scroll copmpressor.
    problem is: the liquid line specialy after sight glass is cold ( near of TXV is colder) and when compressor is started the amperage become High and variable.
    i read an article that said if there is a restriction, the amperage must be low because of starved Evap and low suction pressure.
    whats your idea?
    Apr 2010
    Qatar
    37
    27
    Re: Variable Amperage And Cold Liquid line
    Replace filter drier
    Sep 2014
    Qom
    9
    i did but the problem is not solved
    Sep 2014
    Qom
    9
    unloaded compressor amperage is 13
    loaded is between 30-50 !!!
    seems there is a restriction such as oil in pipes
    do you agree?
    Oct 2001
    Nottingham UK
    5,128
    42
    What is the compressor nameplate running amps?
    If it is running way above the nameplate FLC then it sounds like your compressor is goosed. A blockage will not make the compressor draw that sort of amps.
    I'm back on the Pale
    Sep 2014
    Qom
    9
    copeland scroll ( nominal 30 A )
    so, you think Comp. is down.
    Oct 2001
    Nottingham UK
    5,128
    42
    Megger it to find out.
    2,609
    29
    Suction & discharge pressures at the same time would also be helpful.
    Sep 2014
    Qom
    9
    Discharge 225 psi
    Suction 45 psi
    Amperage between 35 - 50 ( copeland scroll / nominal 30 A)
    Unloaded: 13 A
    And the liquid line is cold specially after sight glass
    Feb 2014
    london
    32
    Was your indoor unit running as heat pump or cooling?
    Have you checked compressor winding?
    After sight glass should be warm subcooled liquid. If its cold that could be a sign short of refrigerant. If you refer to PH chart you will know the compressor will always pull too many amps when its under charged.
    Sep 2014
    Qom
    9
    its a cooling unit and the compressor winding is normal.
    there was problem when the charge was complete.
    plus, the sight glass indicator shows the system is wet.
    after a vacume, the problem was too.
    ( sorry for bad English)
    Jul 2010
    NTH.QLD Australia
    56
    1,762
    27
    Measure the voltage going to the compressor when the compressor is loaded. Iranian supply should be 230 volts at 50 Hertz using single phase. (Source: Google search.)
    Are you using R22? Have you tested the Capacitors?
    The new filter/Drier will help sort the moisture problem but not the compressor.
    Jul 2010
    NTH.QLD Australia
    56
    1,762
    27
    Drawing 30 Amps on any single electrical item at 240 Volts/ 50 HZ is beyond Australian standards. Drawing 30 amps on one phase of a 3 phase compressor is common in industrial applications.
    Sep 2014
    Qom
    9
    Its a 30 tones A/C with r22
    And I changed the drier but the problem is on.
    So I take the comp and sent for Seller to check it
    And I clean all of system.
    But I like to know whats the reason of problem.
    Mar 2009
    U.S.A.
    300
    13
    What voltage system is this thing operating on?
    (1) 30 Amp Scroll on a 30 Ton Chiller for (1) machine comes close to corresponding with a 460V 3 Ph 60 Hz arrangement....On 230 V 50 HZ the current should be a lot higher. What does the entire compressor nameplate read in terms of Voltages and Current?
    Sep 2014
    Qom
    9
    Quote Originally Posted by sterl View Post
    my mistake.
    15 tone is true and nameplate is 380V/ nominal A: 30