Results 1 to 23 of 23
    Apr 2012
    Iraq
    36
    623
    Compressor upper cover inflation !!!!!!!!!!!!
    i got a split as heatpump with burn out compressor
    Its R22 24000 BTU
    after removing the compressor
    i flushed evaporator and condenser and capilary tube with paint thinner (as i do in usually)
    then flushed them with plenty of R22 and
    replaced the filter
    I installed a LG rotary compressor with same specification of the old compressor
    after making vacuum for 30 minutes
    i charged the system according to Gauge reading not by weight
    so the compressor wasn't work normally
    as the liquid line kept icing
    so i removed the compressor from the unit
    then welded a service valve to to its discharge pipe
    then i attached the manifold gauge and closed it
    i switched on the compressor
    so when its reached 300 psi
    its opened internal safety valve
    so i realesed the air from it
    then i switched it on when its reached 300 psi
    the compressor upper cover get inflated
    then i opened the compressor
    Oct 2007
    manchester
    5,639
    45
    Re: Compressor upper cover inflation !!!!!!!!!!!!
    you sure the shell wasnt that shape before?- internal safety would go before max test pressure rating.
    liq line can frost until properly charged.
    think you may have invalidated any warranty claim!
    Apr 2012
    Iraq
    36
    623
    im sure its inflated
    and the charge was nearly complete
    and about the warranty
    there was no waranty
    Auckland
    74
    3,357
    38
    A lot of contamination effect in opened compressor pics. Did the LG replacement have polyester oil in it, could be a cross contamination problem, combined with acid in system from initial R22 compressor failure, combine with paint solvent flushing agent. A real ****tail of chemical inter-action.
    I do not generally get involved with scrolls but some the casing is at discharge pressure, I think. The casings have a design limit of internal pressures before swelling/ bursting, and discharge back to suction internally. They have a maximum compression ratio operating envelop to protect scroll casing from failure.
    May 2010
    Russia
    168
    It's copperization or optical illusion?
    Apr 2012
    Iraq
    36
    623
    the new compressor and the old are R22 refrigerant
    i meantioned that i flushed them with plenty of R22
    so why the upper case inflated
    Apr 2012
    Iraq
    36
    623
    Quote Originally Posted by bigor_2 View Post
    May 2010
    Russia
    168
    it's copper deposition?
    Apr 2012
    Iraq
    36
    623
    yes its copper deposition
    May 2010
    Russia
    168
    This thread is continuation of http://www.refrigeration-engineer.co...ary-compressor or not?
    Apr 2012
    Iraq
    36
    623
    no
    its different one
    Apr 2012
    Iraq
    36
    623
    the one in this thread is LG rotary
    the one that was in the http://www.refrigeration-engineer.co...ary-compressor
    is panasonic
    May 2012
    59
    1,528
    36
    Quote Originally Posted by kefah View Post
    I think that Bigor was asking because if it is copper, where did it come from?
    Copper on the inside of a compressor normally is the result of acidic oil and
    electrolysis normally caused by moisture and contamination.
    Rob
    May 2012
    59
    1,528
    36
    I'm not saying it hasn't distorted the compressor, but I can't see anything
    unusual from the photo I see and I've never heard of a hermetic compressor
    distorting this way from closing a service valve. I did not think it would be possible
    for a scroll compressor to pump high enough pressure for it to fail in the way?
    I'm not saying it can't happen, I have just never heard of it before.
    The only compressors that I know to have distorted were charged
    up with Nitrogen and that was at pressures far in excess of 300psi.
    300psi is nothing in pressure for a compressor like that, it's only 21 bar
    and R22 would reach that at 55 degC?
    That compressor would have to conform to a pressure well in excess of
    40 bar (600psi) for it to be deemed a pressure vessel in the EU and if
    I remember correctly I think it would have to be capable of withstanding
    a temperature that is equal to 100 degC for a certain period of time and
    that is off the scale of R22.
    rob
    Apr 2012
    Iraq
    36
    623
    as i said i removed the compressor from the unit
    then i welded s service valve to its discharge port to it
    i closed the gauge and switched on the compressor
    when the pressure reached 300 psi
    upper case inflated
    3,853
    Maybe it dieseled, think the motor is open to the high side pressure on those, air 300psi it air and oil vapour would make a flammable mixture.
    There was a guy in Africa blew an ac system and compressor apart doing something similar.
    Apr 2012
    Iraq
    36
    623
    this is the most accepted story
    thank u pal
    May 2010
    Russia
    168
    2 kefah
    I'm sorry but I do not quite understand your technology.
    You doing fill the paint thinner into refrigerant circuit?
  19. #19
    Apr 2012
    Iraq
    36
    623
    no man
    i really appreciate your help
    and im sorry for my broken English
    here what i do
    i un weld (remove) the evaporator and condenser and capillary from the unit
    all parts now separeted from each other
    then
    i inject nearly 100 CC of paint thinner into each part
    then i use plent of R22 refrigerant into the parts to remove the paint thinner
  20. #20
    Dec 2008
    563
    Definitely think that you had the remains of the paint thinner along with air/oil mixture in the system, causing an internal explosion, as 30 minutes on the vac pump might not have been long enough to boil off the residue.
    It is really not advisable to use any non compatible cleaners/solvents in refrigeration systems, the chemical mix will eventually cause major operational problems.
    Bedford. Now retired and trying to relax.
  21. #21
    Apr 2012
    Iraq
    36
    623
    Quote Originally Posted by hyperion View Post
    ok
    the inflation happened after i removed the compressor from the unit
    not inside the unit
    so why that didnt happen when i installed new compressor after it
  22. #22
    Oct 2007
    manchester
    5,639
    45
    use of vac pump removes air from system- air is 3 physical properties- 1 being oxygen- kaboom
    http://en.wikipedia.org/wiki/Atmosphere_of_Earth
  23. #23
    Apr 2012
    Iraq
    36
    623
    thank u all