Results 1 to 8 of 8
Thread: High discharge temprature
Hybrid View
-
20-09-2013, 09:55 AM #1
Re: High discharge temprature
1) high suction superheat
2) exp valve not feeding properly
3) short of refrigerant
dd koranne
-
20-09-2013, 10:30 AM #2
Re: High discharge temprature