    What are the causes for high discharge temprature ?
    Feb 2007
    2,473
    45
    Re: High discharge temprature
    High discharge pressure?
    Lack of refrigerant returning to the compressor?
    Incorrect design?
    Apr 2008
    Canada
    253
    4
    May 2006
    India
    74
    399
    1) high suction superheat
    2) exp valve not feeding properly
    3) short of refrigerant
    dd koranne
    Sep 2013
    Philippines
    2
    Another cause of high discharge temperature is the presence on noncondensible gases in the condenser, like air in the system. or maybe there is not enough cooling system for the condenser, it maybe clogged or dirty.
    Mar 2012
    italy
    67
    78
    13
    The compressor off limits,
    coolers does not work,
    high superheat,
    mechanical problems.
    3,357
    mfmsheri,
    Do you have a specific problem, or just general question?
    Is it a screw or reciprocating compressor, which refrigerant & what temperature are you getting.
    Jan 2006
    Croatia
    68
    2,263
    31
    Hi, mfmsheri
    Quote Originally Posted by mfmsheri View Post
    can be a lot of causes ... we need some more particular information to be able to give some suggestion ...
    is your question in relation with this ....
    http://www.refrigeration-engineer.co...il-temperature
    Best regards, Josip