    P17 fault



    Hi guy has any come across P17 fault on a hitachi RAS-8FSG. Cnt find it in manual I have thanks
    Paul



  2. #2
    Join Date
    Dec 2007
    Location
    ireland
    Age
    54
    Posts
    275
    Rep Power
    26

    Re: P17 fault

    Showing up in my book as inverter trip after 3 trips in 20 mins should throw up a code like 51 ,52 ,53.

  3. #3
    Join Date
    Feb 2007
    Location
    UK
    Posts
    2,473
    Rep Power
    45

    Re: P17 fault

    Check the output from the inverter to the compressor, either with an inverter checker or a volt meter. With the compressor disconnected all three phases should be roughly the same when measured to neutral.

    If the inverter is OK then check if the compressor is down to earth.

    If all the above is OK you probably looking at a ciesed compressor.


  4. #4
    Join Date
    Apr 2010
    Location
    Jersey c i
    Posts
    82
    Rep Power
    15

    Re: P17 fault

    Thanks for the help you where spot on the invertor has failed test compressors both ok swapped over the invertor from anther unit which is not being used as floor is empty , all running great now , only need to find a hatichi supplier

  5. #5
    Join Date
    Oct 2007
    Location
    manchester
    Age
    50
    Posts
    5,639
    Rep Power
    45

    Re: P17 fault

    climate ctr can get hitatchi stuff

  6. #6
    Join Date
    Apr 2010
    Location
    Jersey c i
    Posts
    82
    Rep Power
    15

    Re: P17 fault

    Ok thanks il try climate control on monday