Thread: P17 fault
-
26-07-2013, 09:07 AM #1
P17 fault
Hi guy has any come across P17 fault on a hitachi RAS-8FSG. Cnt find it in manual I have thanks
Paul
-
26-07-2013, 11:33 AM #2
Re: P17 fault
Showing up in my book as inverter trip after 3 trips in 20 mins should throw up a code like 51 ,52 ,53.
-
26-07-2013, 02:48 PM #3
Re: P17 fault
Check the output from the inverter to the compressor, either with an inverter checker or a volt meter. With the compressor disconnected all three phases should be roughly the same when measured to neutral.
If the inverter is OK then check if the compressor is down to earth.
If all the above is OK you probably looking at a ciesed compressor.
-
26-07-2013, 07:32 PM #4
Re: P17 fault
Thanks for the help you where spot on the invertor has failed test compressors both ok swapped over the invertor from anther unit which is not being used as floor is empty , all running great now , only need to find a hatichi supplier
-
26-07-2013, 07:43 PM #5
Re: P17 fault
climate ctr can get hitatchi stuff
-
26-07-2013, 08:24 PM #6
Re: P17 fault
Ok thanks il try climate control on monday