    Nov 2012
    38
    2
    Cooling capacity??
    Hi all,
    I'm currently studying building services and have a refrigeration exam on the way.
    Some advised areas to revise and understand are:
    Refrigerant effect
    Coefficient of Performance
    Compressor power
    Cooling capacity.
    I am happy with the first 3 however, I have searched everywhere I can think of, for the cooling capacity without luck. Can anyone point me in the direction of where I can find out about it. As I thought it was the same as the refrigerant effect.
    The question is based on cycles, and all I could find in books and the internet is about plant sizing which from the question im sure is a different meaning.
    Thanks Greg.
    Sep 2003
    ISRAEL
    66
    4,152
    38
    Re: Cooling capacity??
    Cooling capacity is the amount of heat that can be removed by cooling unit.
    Nov 2012
    38
    2
    Once I found the answer I realised I was looking far to deep.
    As you said Chemi, the amount of cooling work done.
    Mass flow rate x Refrigerant effect.
    hookster's Avatar
    hookster is offline Veteran Poster I am starting to push the Mods: of RE
    Apr 2007
    Hampshire
    439
    26
    You need to go back to your basics here.
    I would assume they will base questions on the Log P-H diagram(Mollier). This is the basis to the refrigeration simple cycle.
    The refrigeration consists of the following states.
    Polytropic Compression
    Isobaric cooling (Supercooling included)
    Isenthalpic expansion
    Isobaric expansion - This is your cooling capacity and corresponds to your net cooling capacity.