    TK -3 way valve theory???



    hi guys, i have a question about the TK 3-way valve working theory. Generally, i understand how it works, but in terms of the "condenser Pressure Bypass Check Valve", I was told that it improves 3-way valve heat-to-cool response time, how does that improve it? If there is no this condenser pressure bypass check valve, i didn't see anything difference as it shifts from heat to cool mode? could any one tell me about that in very very details?



  2. #2
    Join Date
    Apr 2006
    Location
    UK
    Age
    55
    Posts
    1,908
    Rep Power
    30

    Re: TK -3 way valve theory???

    Quote Originally Posted by reeferj View Post
    hi guys, i have a question about the TK 3-way valve working theory. Generally, i understand how it works, but in terms of the "condenser Pressure Bypass Check Valve", I was told that it improves 3-way valve heat-to-cool response time, how does that improve it? If there is no this condenser pressure bypass check valve, i didn't see anything difference as it shifts from heat to cool mode? could any one tell me about that in very very details?
    Hi reeferj

    If my memory serves me correctly

    Just like on a cold day when 'if' the system was to run without a cbcv your head pressure would be to low & you would over condensing - starving the txv of a clear feed of liquid

    remember how you partially block the condensor on cold days to check for correct charge on units that do not have cbcv's

    Same thing when it switchs from heat to cool

    It allows the head pressure to build quicker by bypassing the condensor

    And as you need a set pressure at a set temperature to condense

    You in effect go into full cooling mode quicker

    Does that make sense ?
    If the World did not Suck, We would all fall off !

  3. #3
    Join Date
    Mar 2011
    Location
    canada
    Posts
    59
    Rep Power
    14

    Re: TK -3 way valve theory???

    Thanks Chillerman so much, but in the cbcv has two things, one is the bypassing function, which is like what you said, when pilot solenoid closes, it can build up the pressure quickly on the valve condenser side. I understand this function. However, the other thing is the check valve, it only allows ***** to flow from condenser to discharge vibe, it won't work the other way, what is this function? why?

    If it just had the bypassing channel only, no check valve, it seems the valve still works fine, doesn't it?

    When it is in heat or defrost mode, the condenser side of 3-way valve is almost 0 psig or very small pressure, so the check valve always closes, how's that improve the heat-to-cool respond time?

    If I front seat the check valve, no ***** flows, it doesn't make any difference, right?

  4. #4
    Join Date
    Apr 2006
    Location
    UK
    Age
    55
    Posts
    1,908
    Rep Power
    30

    Re: TK -3 way valve theory???

    Quote Originally Posted by reeferj View Post
    Thanks Chillerman so much, but in the cbcv has two things, one is the bypassing function, which is like what you said, when pilot solenoid closes, it can build up the pressure quickly on the valve condenser side. I understand this function. However, the other thing is the check valve, it only allows ***** to flow from condenser to discharge vibe, it won't work the other way, what is this function? why?

    If it just had the bypassing channel only, no check valve, it seems the valve still works fine, doesn't it?

    When it is in heat or defrost mode, the condenser side of 3-way valve is almost 0 psig or very small pressure, so the check valve always closes, how's that improve the heat-to-cool respond time?

    If I front seat the check valve, no ***** flows, it doesn't make any difference, right?
    no prob Mate

    That side of it is just to stop liquid refrigerant flowing back to the 3way valve (will not function full of liquid) when unit stops
    If the World did not Suck, We would all fall off !

  5. #5
    Join Date
    Mar 2011
    Location
    canada
    Posts
    59
    Rep Power
    14

    Re: TK -3 way valve theory???

    stop liquid refrigerant flowing back to 3-way valve? Where is the liquid ***** from? I still didn't get how this check valve's function, and why we need it there.

  6. #6
    Join Date
    Apr 2006
    Location
    UK
    Age
    55
    Posts
    1,908
    Rep Power
    30

    Re: TK -3 way valve theory???

    Hi reeferj

    There are two check valves that stop condensed/liquid refrigerant from flowing back to the 3way valve + compressor

    They are - condensor bypass check valve & condensor check valve

    Not only does the unit condense refrigerant in the condensor but it also condense's refrigerant in the tubework that bypass's the condensor when ever pressures are low enough not to require the use of the condenser

    When you look at a refrigerant compareter/slide rule

    If you look at any given pressure (discharge/suction pressure)

    and then go straight up to the corresponding temperature

    This is the refrigerants saturated temperature

    If you then take a touch probe & measure the tubework (bypassed or condensor outlet etc)

    If the refrigerant is condensed you will have a temperature lower than

    The corresponding temperature on the compareter for that pressure

    If the temperature is equal - it's saturated (as above)

    If it's a higher temperature - its superheated

    Does that make sense mate
    If the World did not Suck, We would all fall off !

  7. #7
    Join Date
    Mar 2011
    Location
    canada
    Posts
    59
    Rep Power
    14

    Re: TK -3 way valve theory???

    Based on what you said, that small check valve in 3-way valve is not necessary part for the system to work. Even in the design, that small check valve in 3-way valve can be taken way and wont' affect the 3-way valve function.

  8. #8
    Join Date
    Mar 2011
    Location
    canada
    Posts
    59
    Rep Power
    14

    Re: TK -3 way valve theory???

    just keep the bypassing tube in 3-way valve, that is enough for the 3-way way. no that small check valve in the 3-way valve and block that, there is no refrigerant migration at all!

  9. #9
    Join Date
    Mar 2011
    Location
    canada
    Posts
    59
    Rep Power
    14

    Re: TK -3 way valve theory???

    let's focus on the small check valve in the 3-way valve. what is its function? if just for stopping liquid refrigeration migration. that why in the designing, it has to be there. why just no this small check in the 3-way valve?

  10. #10
    Join Date
    Apr 2006
    Location
    UK
    Age
    55
    Posts
    1,908
    Rep Power
    30

    Re: TK -3 way valve theory???

    hi reeferj

    If I am understanding your question correctly

    Your talking about the little service valve on the 3way valve

    What that is for is just to check if the 3way valve is sealing or needs a service kit

    How to use it=

    You run the unit and wind in the valve

    immediatly stop the unit & with a jumper wire you energise the pilot solenoid

    whilst watching your discharge gauge

    when the pressure settles

    you de-energise the pilot solenoid

    and watch your discharge gauge

    if the pressure stays stable the 3way valve is working correctly

    If the pressure rises then the 3way valve is letting by & not sealing

    R's chillerman
    If the World did not Suck, We would all fall off !

  11. #11
    Join Date
    Mar 2011
    Location
    canada
    Posts
    59
    Rep Power
    14

    Re: TK -3 way valve theory???

    ohohohohoh, it makes sense, this little check valve is just for checking if 3-way valve works properly or not. it does make sense. it is a tool for our technician. Thank you so much, very very much!!!!!!!!!!!!!!!!!!!!!!!!!!!!!!!!!!!!!!!!!!!!!!!!!!!!!!!!!!!!!!!!!!!!!!!!!!!!!!!!!!!!!!!!!!!!!!!! !!!!!!!!!!!!!!!!!!!!!!!!!!!!!

  12. #12
    Join Date
    Apr 2006
    Location
    UK
    Age
    55
    Posts
    1,908
    Rep Power
    30

    Re: TK -3 way valve theory???

    Quote Originally Posted by reeferj View Post
    ohohohohoh, it makes sense, this little check valve is just for checking if 3-way valve works properly or not. it does make sense. it is a tool for our technician. Thank you so much, very very much!!!!!!!!!!!!!!!!!!!!!!!!!!!!!!!!!!!!!!!!!!!!!!!!!!!!!!!!!!!!!!!!!!!!!!!!!!!!!!!!!!!!!!!!!!!!!!!! !!!!!!!!!!!!!!!!!!!!!!!!!!!!!
    Reeferj

    Absolutely no problem mate

    I am happy to be of assistance

    R's chillerman
    If the World did not Suck, We would all fall off !

  13. #13
    Join Date
    Mar 2009
    Location
    Indiana, USA
    Age
    56
    Posts
    75
    Rep Power
    16

    Re: TK -3 way valve theory???

    Quote Originally Posted by chillerman2006 View Post
    hi reeferj

    If I am understanding your question correctly

    Your talking about the little service valve on the 3way valve

    What that is for is just to check if the 3way valve is sealing or needs a service kit

    How to use it=

    You run the unit and wind in the valve

    immediatly stop the unit & with a jumper wire you energise the pilot solenoid

    whilst watching your discharge gauge

    when the pressure settles

    you de-energise the pilot solenoid

    and watch your discharge gauge

    if the pressure stays stable the 3way valve is working correctly

    If the pressure rises then the 3way valve is letting by & not sealing

    R's chillerman
    That is not why the check valve is there. Earlier 3-way valves did not have this check valve and you could still test the seat this way. It is there for the reason the original poster stated.

  14. #14
    Join Date
    Mar 2011
    Location
    canada
    Posts
    59
    Rep Power
    14

    Re: TK -3 way valve theory???

    hi Boss302, could you explain it in details, please? how does that work?

  15. #15
    Join Date
    Mar 2009
    Location
    Indiana, USA
    Age
    56
    Posts
    75
    Rep Power
    16

    Re: TK -3 way valve theory???

    3 way valve.jpg Hope this helps. I don't believe TK started using the check valve until they started running R502, due to the higher head pressure.

  16. #16
    Join Date
    Apr 2006
    Location
    UK
    Age
    55
    Posts
    1,908
    Rep Power
    30

    Re: TK -3 way valve theory???

    Quote Originally Posted by Boss302 View Post
    That is not why the check valve is there. Earlier 3-way valves did not have this check valve and you could still test the seat this way. It is there for the reason the original poster stated.
    My Mistake
    Last edited by chillerman2006; 19-08-2011 at 01:54 AM.
    If the World did not Suck, We would all fall off !

  17. #17
    Join Date
    Mar 2009
    Location
    Indiana, USA
    Age
    56
    Posts
    75
    Rep Power
    16

    Re: TK -3 way valve theory???

    The "Little service valve on the 3-way valve" is part of the condenser pressure bypass check valve. I believe you didn't read the post properly. That is what he asked about. The check valve is not there for checking the 3-way valve for functioning correctly. I understood exactly what he was asking about.

  18. #18
    Join Date
    Apr 2006
    Location
    UK
    Age
    55
    Posts
    1,908
    Rep Power
    30

    Re: TK -3 way valve theory???

    Quote Originally Posted by Boss302 View Post
    The "Little service valve on the 3-way valve" is part of the condenser pressure bypass check valve. I believe you didn't read the post properly. That is what he asked about. The check valve is not there for checking the 3-way valve for functioning correctly. I understood exactly what he was asking about.
    Well after your post here, as I have not touched one for 15 years (dirty work moved on up), double checked with ThermoKing Engineers that I worked with & still see often, both said the same thing, Strange

    Plus I have carried this procedure out at least 300 times, on annual/major services, it works try it !
    Last edited by chillerman2006; 17-08-2011 at 02:39 PM.
    If the World did not Suck, We would all fall off !

  19. #19
    Join Date
    Nov 2010
    Location
    The Netherlands
    Age
    64
    Posts
    134
    Rep Power
    14

    Re: TK -3 way valve theory???

    Boss302 is on the button. The condensor pressure bypass check valve was fitted to improve heating/defrost and three way valve response time, during the introduction of higher pressure refrigerants. You don't close the check valve to test the three way valve, you close it because otherwise you can't test the three way valve.

  20. #20
    Join Date
    Apr 2006
    Location
    UK
    Age
    55
    Posts
    1,908
    Rep Power
    30

    Re: TK -3 way valve theory???

    Quote Originally Posted by Robert Hilton View Post
    You don't close the check valve to test the three way valve, you close it because otherwise you can't test the three way valve.
    Well that makes good sense- you still have to close it

    The op asked about the check valves then last time asked again from a different angle (I only speak plain english which that is not), reading the post it appears he wants another answer, he got one, which explains how to test 3way valve

    I worked for TK for 3 years & succesfully faulted valves with this procedure, replaced the kits & then it works/seals

    I also worked for Carrier (united technologies) & when they brought out the Vector that was the end of the engineer...all they do now is change oil/filters & sensors, no technical abillity needed no more as a vector will compensate so well it will pull chilled with half a charge of refigerant and tell you whats wrong with it!
    If the World did not Suck, We would all fall off !

  21. #21
    Join Date
    Jan 2008
    Location
    Texas
    Age
    65
    Posts
    132
    Rep Power
    17

    Re: TK -3 way valve theory???

    Straight from the book

    Condenser Pressure Bypass Check Valve: A valve
    located in the 3-way valve end cap. It permits condenser
    pressure to flow to the discharge line when the 3-way valve
    first shifts to heat. It improves the 3-way valve response
    time when the pilot solenoid closes.

  22. #22
    Join Date
    Nov 2009
    Location
    Canada
    Posts
    123
    Rep Power
    15

    Re: TK -3 way valve theory???

    Quote Originally Posted by chillerman2006 View Post

    I also worked for Carrier (united technologies) & when they brought out the Vector that was the end of the engineer...all they do now is change oil/filters & sensors, no technical abillity needed no more as a vector will compensate so well it will pull chilled with half a charge of refigerant and tell you whats wrong with it!

    Is that so...well i hope your T/K buddies don't read that.. i was sent a Vector form a customer that T/K couldn't fix...................i won't tell you what the fault was........but it certainly didn't tell you what it was !!!!!!! that could be one for quote of the year
    Last edited by moggy66; 18-08-2011 at 04:21 AM.

  23. #23
    Join Date
    Apr 2006
    Location
    UK
    Age
    55
    Posts
    1,908
    Rep Power
    30

    Re: TK -3 way valve theory???

    Quote Originally Posted by DaButcher View Post
    Straight from the book

    Condenser Pressure Bypass Check Valve: A valve
    located in the 3-way valve end cap. It permits condenser
    pressure to flow to the discharge line when the 3-way valve
    first shifts to heat. It improves the 3-way valve response
    time when the pilot solenoid closes.
    the book i give away 15 tears ago when i got bored of that game, not argueing thats wrong, i told the fella how to check 3 way valve, and got told its wrong

    A common cbcv works as i described earlier & recall that easier as the bleed valve

    Human Nature
    Last edited by chillerman2006; 18-08-2011 at 11:06 AM.
    If the World did not Suck, We would all fall off !

  24. #24
    Join Date
    Apr 2006
    Location
    UK
    Age
    55
    Posts
    1,908
    Rep Power
    30

    Re: TK -3 way valve theory???

    Quote Originally Posted by moggy66 View Post
    Is that so...well i hope your T/K buddies don't read that.. i was sent a Vector form a customer that T/K couldn't fix...................i won't tell you what the fault was........but it certainly didn't tell you what it was !!!!!!! that could be one for quote of the year
    I'm uk not canada
    Last edited by chillerman2006; 19-08-2011 at 03:09 AM.
    If the World did not Suck, We would all fall off !

  25. #25
    Join Date
    Apr 2006
    Location
    UK
    Age
    55
    Posts
    1,908
    Rep Power
    30

    Re: TK -3 way valve theory???

    always look on the bright side of life, di de, di de di de di de

    PS. Marshall ThermoKing, kick a** here, they fix anything!!!

    Vectors for breakfast
    Last edited by chillerman2006; 18-08-2011 at 11:24 AM.
    If the World did not Suck, We would all fall off !

  26. #26
    Join Date
    Apr 2006
    Location
    UK
    Age
    55
    Posts
    1,908
    Rep Power
    30

    Re: TK -3 way valve theory???

    boss, robert, butcher & moggy

    dont take things so seriously

    let your hair down, chill out & just have a laugh

    (remember human nature & I'm knocking on now)

    come join in & let us here it from the other side of the fence

    http://www.refrigeration-engineer.co...at-Us-This-Way
    If the World did not Suck, We would all fall off !

  27. #27
    Join Date
    Apr 2006
    Location
    UK
    Age
    55
    Posts
    1,908
    Rep Power
    30

    Re: TK -3 way valve theory???

    Quote Originally Posted by moggy66 View Post
    i was sent a Vector form a customer that T/K couldn't fix..................
    " a vector form " it's just a tick sheet ... you know pen to paper .... Tick
    If the World did not Suck, We would all fall off !

  28. #28
    Join Date
    Jan 2008
    Location
    Canada
    Posts
    579
    Rep Power
    17

    Re: TK -3 way valve theory???

    Quote Originally Posted by chillerman2006 View Post
    well it just shows the standard of your people, I'm uk not canada



    so its your people not mine





    hahahahaha good night

    Buddy, I'm from Canada and proud of it. I know my stuff and can fix, yes I said fix, anything properly too. I take offence to what your saying here especialy considdering you are contradicting yourself constantly. Read this post from the start. You should be commended for trying to help. That said, once you were corrected, you started to spew garbage like a child.
    Case in point, you say "I also worked for Carrier (united technologies) & when they brought out the Vector that was the end of the engineer...all they do now is change oil/filters & sensors, no technical abillity needed no more as a vector will compensate so well it will pull chilled with half a charge of refigerant and tell you whats wrong with it!"
    Then you say " PS. Marshall ThermoKing, kick a** here, they fix anything!!!

    Vectors for breakfast
    "

    What do you mean? They are good at dumping oil? Have you ever even worked on a Vector?
    Anyways, I'm not here to insult.
    I would just like to thank you for giving an effort but encourage you to open your mind and accept that others may know more than you. If your not carefull you may learn something from these guys. They are a great bunch. I can vouch for that.
    Cheers boys!
    Last edited by abbsnowman; 18-08-2011 at 09:17 PM. Reason: spelling

  29. #29
    Join Date
    Apr 2006
    Location
    UK
    Age
    55
    Posts
    1,908
    Rep Power
    30

    Re: TK -3 way valve theory???

    unless my history teacher was misstaken aswell as me

    Were it not, apart from the red indians(dont know their background) everyone in america traces back to europe & everyone in europe traces back to africa ..... we are all one .....

    we are all the same !!!!

    Dont take things personal,

    I'm just a southern panzie to the tough boys up north .... i dont cry about it

    Lifes to short to give a s h- ite about silly things

    have a laugh and live every day as if its your last as one day it will be

    Oh! and yes I have worked on them(vector 1 & 2), and done the coarse after I finished throwing up from the too many drinks from the night before, just missed the first hour, but I caught up
    Last edited by chillerman2006; 19-08-2011 at 03:10 AM.
    If the World did not Suck, We would all fall off !

  30. #30
    Join Date
    Apr 2006
    Location
    UK
    Age
    55
    Posts
    1,908
    Rep Power
    30

    Re: TK -3 way valve theory???

    Quote Originally Posted by abbsnowman View Post
    Buddy, you started to spew garbage like a child.
    Case in point, you say "I also worked for Carrier (united technologies) & when they brought out the Vector that was the end of the engineer...all they do now is change oil/filters & sensors, no technical abillity needed no more as a vector will compensate so well it will pull chilled with half a charge of refigerant and tell you whats wrong with it!"
    Then you say " PS. Marshall ThermoKing, kick a** here, they fix anything!!!

    Vectors for breakfast
    "

    What do you mean? They are good at dumping oil? Have you ever even worked on a Vector?
    Anyways, I'm not here to insult.
    I would just like to thank you for giving an effort but encourage you to open your mind and accept that others may know more than you. If your not carefull you may learn something from these guys. !
    Cant handle my drink! was tea-total till you's started picking on me

    Marshall's can fix anything...thats were everyone goes when their local firm cant fix it, and they get it sorted some real top engineers there & technical backup they have is second to none

    I do believe the vector has resulted in lost jobs due to self diagnostics & much quicker to do maintenance just oil/filters & usual checks, no belts/pulleys, which has reduced time it takes. Plus has made them super reliable. Once the teething poblems were sorted, chargers & generators, still have sensor problems so I hear.

    Spew like a child - I dont want to insult either

    If I missed a bit let me know & I'll be back tomorrow as I have to go fishing to sort out next weeks nosh, got one for this weekend, and now we are such close friends I know I can trust you not too tell my mrs
    Last edited by chillerman2006; 19-08-2011 at 03:15 AM.
    If the World did not Suck, We would all fall off !

  31. #31
    Join Date
    Oct 2007
    Location
    manchester
    Age
    50
    Posts
    5,639
    Rep Power
    45

    Re: TK -3 way valve theory???

    chillerman -she needs a new thrust bearing and an oil change,just seen her leaving the fire station with ur misses and they were hobbling like john wayne!haha

  32. #32
    Join Date
    Apr 2006
    Location
    UK
    Age
    55
    Posts
    1,908
    Rep Power
    30

    Re: TK -3 way valve theory???

    Damn!! I bet mr bartlett was there as well, grinning like a cheshire cat (apologies cat lovers & cheshire - got enough complaints here dont need no more)

    #14 & #17 of

    http://www.refrigeration-engineer.co...algae-and-moss

    See I can take it !

    ps .. core would do that celine dion, dont know any others
    Last edited by chillerman2006; 18-08-2011 at 10:44 PM.
    If the World did not Suck, We would all fall off !

  33. #33
    Join Date
    Apr 2006
    Location
    UK
    Age
    55
    Posts
    1,908
    Rep Power
    30

    Re: TK -3 way valve theory???

    Gents

    you might find this post explains it all

    http://www.refrigeration-engineer.co...178#post237178

    or this one

    http://www.refrigeration-engineer.co...170#post237170

    You wont feel as touchy & might even learn something
    If the World did not Suck, We would all fall off !

  34. #34
    Join Date
    Oct 2007
    Location
    manchester
    Age
    50
    Posts
    5,639
    Rep Power
    45

    Re: TK -3 way valve theory???

    wasnt celine dion born COLIN DION ???

  35. #35
    Join Date
    Apr 2006
    Location
    UK
    Age
    55
    Posts
    1,908
    Rep Power
    30

    Re: TK -3 way valve theory???

    Quote Originally Posted by install monkey View Post
    wasnt celine dion born COLIN DION ???
    I remember hearing something like that years ago maybe moggy knows !
    If the World did not Suck, We would all fall off !

  36. #36
    Join Date
    Oct 2007
    Location
    manchester
    Age
    50
    Posts
    5,639
    Rep Power
    45

    Re: TK -3 way valve theory???

    as long as it shaves its bum,port and storm spring to mind!

  37. #37
    Join Date
    Mar 2009
    Location
    Indiana, USA
    Age
    56
    Posts
    75
    Rep Power
    16

    Re: TK -3 way valve theory???

    Quote Originally Posted by chillerman2006 View Post
    i told the fella how to check 3 way valve, and got told its wrong
    I never said that isn't how you check the 3 way valve. I was just trying to help the original poster. I could see him getting easily confused about the check valve. Seemed to me that he was thinking the check valve/service valve was just there to check the 3 way valve.

  38. #38
    Join Date
    Apr 2006
    Location
    UK
    Age
    55
    Posts
    1,908
    Rep Power
    30

    Re: TK -3 way valve theory???

    Quote Originally Posted by Boss302 View Post
    I never said that isn't how you check the 3 way valve. I was just trying to help the original poster. I could see him getting easily confused about the check valve. Seemed to me that he was thinking the check valve/service valve was just there to check the 3 way valve.
    Good evening Boss

    I missread the post - My Mistake - twice
    If the World did not Suck, We would all fall off !

  39. #39
    Join Date
    Nov 2010
    Location
    The Netherlands
    Age
    64
    Posts
    134
    Rep Power
    14

    Re: TK -3 way valve theory???

    The only thing I have learned in two days is how quick my ribs & cheeks can compress !

    I smell troll.

  40. #40
    Join Date
    Apr 2006
    Location
    UK
    Age
    55
    Posts
    1,908
    Rep Power
    30

    Re: TK -3 way valve theory???

    Quote Originally Posted by Robert Hilton View Post
    I smell
    Good Evening Robert

    There are no Gas Sensors on here so if you kept it quiet, no-one would have known !
    If the World did not Suck, We would all fall off !

  41. #41
    Join Date
    Mar 2011
    Location
    canada
    Posts
    59
    Rep Power
    14

    Re: TK -3 way valve theory???

    oh, fire!fire!!!!!!!fire!!!!!!!!!!!!!!!!!!

  42. #42
    Join Date
    Mar 2011
    Location
    canada
    Posts
    59
    Rep Power
    14

    Re: TK -3 way valve theory???

    anyway, thanks everyone for joining this stuff...........just for very technical problem, no personal ones! thanks!!

  43. #43
    Join Date
    Mar 2011
    Location
    canada
    Posts
    59
    Rep Power
    14

    Re: TK -3 way valve theory???

    after i think it over again, that cbcv works this way: let's say it is running at cool mode now, when heating is called, pilot solenoid is energized, the pressure at spring side is released, so the condenser pressure can push the piston against the spring pressure, so that the 3-way shifts to heat mode;

    at this moment, if there is no cbcv to release the pressure to discharge vibe, which means that high condenser pressure always stays in the condenser to be against the piston, whenever cooling is called, solenoid is closed, the pressure at spring side has to be built up for a while until two pressures (spring's & discharge's) are big enough to push the 3-way piston to evap's side.

    If cbcv exists, it release condenser's pressure to discharge vibe in heat mode, which lowers condenser pressure so much, so that two pressure (spring's & discharge's) can easily overcome condenser pressure, which improves the respond time in heat-to-cool mode.

    I think I am right this time!!!!!

  44. #44
    Join Date
    Jun 2004
    Location
    Finland
    Posts
    136
    Rep Power
    20

    Re: TK -3 way valve theory???

    Hi,

    I think reeferj got it right. Also if we have truck unit with TherMax, cpbv is useless as thermax solenoid bleeds pressure from condenser.


    -nova-

  45. #45
    Join Date
    Mar 2009
    Location
    Indiana, USA
    Age
    56
    Posts
    75
    Rep Power
    16

    Re: TK -3 way valve theory???

    Sounds like you got it now Reeferj

  46. #46
    Join Date
    Apr 2006
    Location
    UK
    Age
    55
    Posts
    1,908
    Rep Power
    30

    Re: TK -3 way valve theory???

    Off topic - needed removing