    Panasonic CS-E9DKRW / CU-E9DKR Inverter H16 Error Code



    Hi.

    Over the last little while I have noticed that the outdoor unit seems to be ramping up and down a lot when in operation (heating). usually it just ticks along once up to temperature. Last night was the coldest night we have had this winter and got to around -1 degC frost outside. This morning the indoor unit Timer led was flashing.

    The only error code is H16 which looks like it can be one of three things "Power Transistor Module or Outdoor PCB Faulty. Very Low Gas"

    I had a problem with low gas last summer where the unit wasn't cooling. the installer found a cracked brass fitting where the piping connected to the indoor unit pipes.

    I have powered the unit on & off and it is running again. The outdoor unit does seem to be running pretty hard for the amount of heat coming out of the indoor unit though.
    Before calling in the installer I would like to do some homework myself and would appreciate some comments from those with some experience.

    1. Given the cold night and the outdoor unit ramping up/down is it likely to be an electronics problem or Very low gas?

    2. Is there no warning or error code for low gas pressure without another fault?

    3. I believe the unit remembers the last 3 or 4 errors, how do I check for previous errors?

    4. the document I have seen says "Fault Codes are cleared from memory by setting Test Cooling and shorting the RESET terminals in the controller battery compartment."

    I don't see any Reset terminals in the controller battery compartment. only the recessed "Check" and "Reset" buttons. The Reset button only seems to reset the remote control to default values.

    Regards Allen.



  2. #2
    Join Date
    Jul 2011
    Location
    New Zealand
    Posts
    6
    Rep Power
    0

    Re: Panasonic CS-E9DKRW / CU-E9DKR Inverter H16 Error Code

    Hi.

    Is there really no one who can offer advice please?

  3. #3
    Join Date
    Sep 2007
    Location
    Split Croatia
    Age
    57
    Posts
    6,151
    Blog Entries
    6
    Rep Power
    36

    Re: Panasonic CS-E9DKRW / CU-E9DKR Inverter H16 Error Code

    With inverters is little difficult to give advice to non-professional.
    My first advice is to call technician that he recover and weigh refrigerant.
    That would be starting point for further steps.

  4. #4
    Join Date
    Jul 2011
    Location
    New Zealand
    Posts
    6
    Rep Power
    0

    Re: Panasonic CS-E9DKRW / CU-E9DKR Inverter H16 Error Code

    Thanks for the reply. Given the unit resets and runs and only shuts off on the coldest nights and the outdoor unit ramping up/down does this suggest very low gas?

    I'm an electrical technician and like try and understand whats likely to be going on so I can recognize when the installer is trying in on with "The compressor is stuffed" when it's only low gas?

    Appreciate the help.

    Regards Allen.

  5. #5
    Join Date
    Apr 2006
    Location
    UK
    Age
    55
    Posts
    1,908
    Rep Power
    30

    Re: Panasonic CS-E9DKRW / CU-E9DKR Inverter H16 Error Code

    Quote Originally Posted by AllenG View Post
    I'm an electrical technician
    No disrespect meant Allen, but from what i read on this site and from friends in Oz, thats the big problem in Oz & New Zealand

    Non refrigeration techs, getting a little knowledge and then an Artick Licence

  6. #6
    Join Date
    Sep 2007
    Location
    Split Croatia
    Age
    57
    Posts
    6,151
    Blog Entries
    6
    Rep Power
    36

    Re: Panasonic CS-E9DKRW / CU-E9DKR Inverter H16 Error Code

    [QUOTE]
    Quote Originally Posted by AllenG View Post
    Thanks for the reply. Given the unit resets and runs and only shuts off on the coldest nights and the outdoor unit ramping up/down does this suggest very low gas?
    On inverter it can suggest many things. Also, any air-conditioner is struggling between 0 and +5°C when humidity is high. Beyond that, it could run perfectly smooth even till -15°C.

    I'm an electrical technician and like try and understand whats likely to be going on so I can recognize when the installer is trying in on with "The compressor is stuffed" when it's only low gas?

    Appreciate the help.

    Regards Allen.
    Therefore you should call service tehnician, not installer. Diference is huge.

  7. #7
    Join Date
    Jul 2011
    Location
    New Zealand
    Posts
    6
    Rep Power
    0

    Re: Panasonic CS-E9DKRW / CU-E9DKR Inverter H16 Error Code

    Quote Originally Posted by chillerman2006 View Post
    Non refrigeration techs, getting a little knowledge and then an Artick Licence
    This is my own equipment I'm trying to understand. I'm not about to get into the refrigeration business.

  8. #8
    Join Date
    Jul 2011
    Location
    New Zealand
    Posts
    6
    Rep Power
    0

    Re: Panasonic CS-E9DKRW / CU-E9DKR Inverter H16 Error Code

    [QUOTE=nike123;235923]
    Therefore you should call service tehnician, not installer. Diference is huge.
    OK. Where I live in New Plymouth , NZ they are likely to be the same people.

  9. #9
    Join Date
    May 2008
    Location
    New Zealand
    Posts
    35
    Rep Power
    0

    Re: Panasonic CS-E9DKRW / CU-E9DKR Inverter H16 Error Code

    Think you need to call someone if it is still under warantee, could be something as easy as sensor or something more serious. Unless you are experienced you realy dont want to be tinkering. How old as the unit,

  10. #10
    Join Date
    Feb 2008
    Location
    QLD
    Age
    54
    Posts
    74
    Rep Power
    17

    Re: Panasonic CS-E9DKRW / CU-E9DKR Inverter H16 Error Code

    It should stillbe under warranty, call Panasonic NZ or follow the instructions on your warranty card.
    And I suspect you will be up for a new compressor :-)

  11. #11
    Join Date
    Jul 2011
    Location
    New Zealand
    Posts
    6
    Rep Power
    0

    Re: Panasonic CS-E9DKRW / CU-E9DKR Inverter H16 Error Code

    Quote Originally Posted by phil Landon View Post
    How old as the unit,
    5 years. I think the Warrany is supposed to be 5 years. Just out of warranty.

    Allen.

  12. #12
    Join Date
    May 2008
    Location
    New Zealand
    Posts
    35
    Rep Power
    0

    Re: Panasonic CS-E9DKRW / CU-E9DKR Inverter H16 Error Code

    Give Climate a call as they are the local agents in New Plymouth. See what they say. Might be cheaper to get a new unit if the comp has failed. If it isnt to far out of warrantee they may still do the repairs. Panasonic rely on the installer to tell them when the unit was installed as they dont really keep that info like Toshiba and Carrier and even Fujitsu. Might be worth them coming around and having a look anyhow