Results 1 to 14 of 14
    Feb 2009
    telford
    1,982
    26
    sight glass location
    with refrigerants that are blends [4 series] where in the liquid line on a average system with a pipe run of say 5 metres should you locate it because i have different opinions from my other engineer friends?
    Aug 2009
    New Zealand
    2,556
    Re: sight glass location
    Quote Originally Posted by cadwaladr View Post
    You should ask your self, what is the sight glass used for? moisture indicator and refrigerant flow.
    As far as system charge goes it is an "aid" to charging and not a method.
    What do you "not" want see in the sight glass, and why?
    Answer the why, and this will give you the correct position. (and it is not where every body mounts them!!!)
    Sep 2003
    ISRAEL
    66
    4,118
    38
    You can use a few sight glasses, after the drier will help you know when it is starting getting blocked. Just before the TXV will help you know if it fed with liquid.
    On oil return line, will indicate flow of oil back to the sump.
    Oct 2007
    manchester
    44
    5,707
    normally there by the condenser so the muppet bomb charging it can see a full sight glass. but they should be located at he tev inlet to ensure no flash gas in the liq line prior to the tev
    Aug 2009
    New Zealand
    2,556
    Quote Originally Posted by install monkey View Post
    And give this dog a bone! or should I say give this monkey a banana
    Oct 2007
    manchester
    44
    5,707
    yay!-if only i could have a rep point haha
    Oct 2003
    56
    5,519
    28
    Chemi was first ;-)
    Nov 2009
    Minsk, Belarus
    32
    164
    9
    But he wasn't say about location before solenoid or after
    In some places will have to think ...
    Dec 2008
    Portugal
    42
    1,039
    13
    Quote Originally Posted by Aik View Post
    Considering the solenoid is just near the TEV I would put it after the solenoid (between the solenoid and the TEV), as this one also create a pressure drop 0,4...1 bar, more or less.
    As mad fridgie said at the first email unfortunately many people don't apply the sight glass on this place. I try to fight that but it's not easy.
    Oct 2003
    56
    5,519
    28
    Half a banana then
    Nov 2009
    Minsk, Belarus
    32
    164
    9
    I prefer put sight glass after filter but before solenoid.
    I also don't put it at that place, only if I have problems with liquid refrigerant circulation, but it's infrequent cases.
    Half a banana then
    Oct 2003
    56
    5,519
    28
    Quote Originally Posted by Sandro Baptista View Post
    Considering the solenoid is just near the TEV I would put it after the solenoid (between the solenoid and the TEV), as this one also create a pressure drop 0,4...1 bar, more or less...
    I should say 0.15 bar is more commonly. If you have 1 bar, then your SV was undersized
    Nov 2009
    Minsk, Belarus
    32
    164
    9
    Yeah, you are right. For example danfoss (servo) solenoid needs minimum 0.05 bar to work well... 1 bar is to much
    Dec 2008
    Portugal
    42
    1,039
    13
    Sorry, you are right. I meant 0,04...0,1 bar.