    Apr 2011
    India
    30
    94
    8
    PH level of water and chemical solution - Descaling
    Dear Friends ,
    How much PH value of solution of water and chemical should be maintained while doing the De-scaling of condensers. If the solution is more acidic , it will damage the copper tubes and if its less then will not remove the scale effectively.
    70
    10,626
    52
    Re: PH level of water and chemical solution - Descaling
    I think that it may depend on the product being used, the following link refers to a particular brand but shows PH levels between 0.5 and 0.7 for the different options.
    Perhaps ask your chemical supplier.
    http://descale.me/downloads/document...Exchangers.pdf
    May 2006
    India
    68
    400
    13
    While plant operates , maintain the following parameters to avoid regular de-scaling
    1) maintain alkaline ph .. 7+
    2) address dissolved oxygen issue by additives ...... To avoid tubes pitting
    3) maintain commercial hardness of cooling water around 5
    4) provide tower bleed-off
    5) maintain tower hygene
    this will give you exceleent results on condenser life & plant perfformance . This will avoid sudden failures