    Re: Excessive contactor Chatter

    The most common cause is foreign contaminates between the magnet and armature. You can remove the coil and clean these contaminates using air or alcohol. Be sure all power is off before attempting this.

  2. #2
    Join Date
    Apr 2009
    Location
    israel
    Age
    50
    Posts
    778
    Rep Power
    19

    Re: Excessive contactor Chatter

    Quote Originally Posted by sachin230 View Post
    The most common cause is foreign contaminates between the magnet and armature. You can remove the coil and clean these contaminates using air or alcohol. Be sure all power is off before attempting this.
    HI I have to agree if there is no evident control problem,this problem is usualy due to dirt or shavings or even bugs inside the contactor,if the contactor is just buzzing all said regarding is true,if the contactor is actully chattering ,you should check control sys excpecially a loose neutral,or bad relay contact.
    good luck
    THE DEFINITION OF A SMART PERSON IS ONE WHOM LEARNS FROM HIS MISTAKES!!!

Similar Threads

  1. excessive superheat orifice help
    By Contactor in forum Fundamentals
    Replies: 4
    Last Post: 17-06-2010, 08:08 PM
  2. excessive airflow, effecting heat exchange
    By chillyblue in forum Air Conditioning
    Replies: 33
    Last Post: 10-11-2009, 08:29 PM
  3. York Chiller Excessive Purges Problem
    By imranmd in forum Commercial
    Replies: 5
    Last Post: 07-03-2008, 05:13 AM
  4. Excessive Frosting on the Evaporator
    By vadivelan in forum Fundamentals
    Replies: 5
    Last Post: 23-06-2007, 12:18 PM
  5. Excessive Superheat
    By AEGIS Cool in forum Technical Discussions
    Replies: 13
    Last Post: 26-11-2006, 08:06 PM

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •