    Excessive contactor Chatter
    I have a Carrier RTU 48TJE012-521 208/230 3ph that I can't seem to find the reason why one of the comp. contactors chatter so bad it will eventually brake apart like the other one did when I arrived on the first call to this unit. but when I remove the 3ph comp. wiring from the comp. and power the rtu back up, that contactor pulls in and is fine (no more excessive chatting). I have the same ohms across the three terminal and nothing to ground and when it does run shortly before the contactor chatters badly I'm pulling about the same amp as the other comp. What would make that contactor chatter so excessive that it will eventually brake apart. Any ideas?
    J
    Split Croatia
    6,106
    7
    30
    Re: Excessive contactor Chatter
    High drop of power supply voltage caused by insufficient cross section of supply cable or/and high load of local power supply transformer.
    Feb 2009
    telford
    2,009
    27
    what is the coil voltage of the contactor
    44
    3,795
    38
    Faulty hp switch pulsing on and off with the discharge from the comp, have seen it a couple of times on refrigeration systems.
    Sep 2008
    430
    14
    Maybe a faulty auxillary contactor if fitted. I`ve come across this before on compressors especially if the control voltage is low, eg 24v, and the enviroment dusty.
    Auckland
    68
    3,362
    31
    Have you had a multi meter across the contactor coil terminals while the chattering is happening. Generally the chattering is because the supply votage is too low to hold the contactor coil in position. It would seem the control circuit supply transformer is dropping output voltage due to system loads, no compressor load the transformer is fine. As Nike said earlier voltage drop in system. You will probably find the control circuit transformer is 2or 3 phase primary and low voltage output/secondary. No compressor load and the transformer is fine. Try replacing the transformer.
    Mar 2010
    India
    101
    9
    The most common cause is foreign contaminates between the magnet and armature. You can remove the coil and clean these contaminates using air or alcohol. Be sure all power is off before attempting this.
    Jul 2010
    South coast nsw
    35
    9
    Gauges on? Check LP HP switch as above mentioned if auto reset
    Apr 2009
    israel
    44
    778
    13
    Quote Originally Posted by sachin230 View Post
    HI I have to agree if there is no evident control problem,this problem is usualy due to dirt or shavings or even bugs inside the contactor,if the contactor is just buzzing all said regarding is true,if the contactor is actully chattering ,you should check control sys excpecially a loose neutral,or bad relay contact.
    good luck
    THE DEFINITION OF A SMART PERSON IS ONE WHOM LEARNS FROM HIS MISTAKES!!!
  1. excessive superheat orifice help
    By Contactor in forum Fundamentals
    Last Post: 17-06-2010, 08:08 PM
  2. excessive airflow, effecting heat exchange
    By chillyblue in forum Air Conditioning
    Last Post: 10-11-2009, 08:29 PM
  3. York Chiller Excessive Purges Problem
    By imranmd in forum Commercial
    Last Post: 07-03-2008, 05:13 AM
  4. Excessive Frosting on the Evaporator
    By vadivelan in forum Fundamentals
    Last Post: 23-06-2007, 12:18 PM
  5. Excessive Superheat
    By AEGIS Cool in forum Technical Discussions
    Last Post: 26-11-2006, 08:06 PM