    Excessive contactor Chatter


    I have a Carrier RTU 48TJE012-521 208/230 3ph that I can't seem to find the reason why one of the comp. contactors chatter so bad it will eventually brake apart like the other one did when I arrived on the first call to this unit. but when I remove the 3ph comp. wiring from the comp. and power the rtu back up, that contactor pulls in and is fine (no more excessive chatting). I have the same ohms across the three terminal and nothing to ground and when it does run shortly before the contactor chatters badly I'm pulling about the same amp as the other comp. What would make that contactor chatter so excessive that it will eventually brake apart. Any ideas?

    J



  2. #2
    Join Date
    Sep 2007
    Location
    Split Croatia
    Age
    48
    Posts
    5,938
    Blog Entries
    5
    Rep Power
    21

    Re: Excessive contactor Chatter

    High drop of power supply voltage caused by insufficient cross section of supply cable or/and high load of local power supply transformer.
    Last edited by nike123; 04-07-2010 at 08:18 PM.
    Now, when I am officialy citizen off EU, I am looking for decent job! For any job offer please check my profile!

  3. #3
    Join Date
    Feb 2009
    Location
    telford
    Posts
    1,209
    Rep Power
    13

    Re: Excessive contactor Chatter

    what is the coil voltage of the contactor

  4. #4
    Join Date
    Aug 2006
    Location
    england
    Age
    40
    Posts
    3,458
    Rep Power
    27

    Re: Excessive contactor Chatter

    Faulty hp switch pulsing on and off with the discharge from the comp, have seen it a couple of times on refrigeration systems.

  5. #5
    Join Date
    Sep 2008
    Location
    england
    Posts
    421
    Rep Power
    10

    Re: Excessive contactor Chatter

    Maybe a faulty auxillary contactor if fitted. I`ve come across this before on compressors especially if the control voltage is low, eg 24v, and the enviroment dusty.

  6. #6
    Join Date
    May 2007
    Location
    Auckland
    Age
    64
    Posts
    2,918
    Rep Power
    19

    Re: Excessive contactor Chatter

    Have you had a multi meter across the contactor coil terminals while the chattering is happening. Generally the chattering is because the supply votage is too low to hold the contactor coil in position. It would seem the control circuit supply transformer is dropping output voltage due to system loads, no compressor load the transformer is fine. As Nike said earlier voltage drop in system. You will probably find the control circuit transformer is 2or 3 phase primary and low voltage output/secondary. No compressor load and the transformer is fine. Try replacing the transformer.

  7. #7
    Join Date
    Mar 2010
    Location
    India
    Posts
    101
    Rep Power
    5

    Re: Excessive contactor Chatter

    The most common cause is foreign contaminates between the magnet and armature. You can remove the coil and clean these contaminates using air or alcohol. Be sure all power is off before attempting this.

  8. #8
    Join Date
    Jul 2010
    Location
    South coast nsw
    Age
    31
    Posts
    10
    Rep Power
    0

    Re: Excessive contactor Chatter

    Gauges on? Check LP HP switch as above mentioned if auto reset

  9. #9
    Join Date
    Apr 2009
    Location
    israel
    Age
    41
    Posts
    758
    Rep Power
    9

    Re: Excessive contactor Chatter

    Quote Originally Posted by sachin230 View Post
    The most common cause is foreign contaminates between the magnet and armature. You can remove the coil and clean these contaminates using air or alcohol. Be sure all power is off before attempting this.
    HI I have to agree if there is no evident control problem,this problem is usualy due to dirt or shavings or even bugs inside the contactor,if the contactor is just buzzing all said regarding is true,if the contactor is actully chattering ,you should check control sys excpecially a loose neutral,or bad relay contact.
    good luck
    THE DEFINITION OF A SMART PERSON IS ONE WHOM LEARNS FROM HIS MISTAKES!!!

Similar Threads

  1. excessive superheat orifice help
    By Contactor in forum Fundamentals
    Replies: 4
    Last Post: 17-06-2010, 08:08 PM
  2. excessive airflow, effecting heat exchange
    By chillyblue in forum Air Conditioning
    Replies: 33
    Last Post: 10-11-2009, 09:29 PM
  3. York Chiller Excessive Purges Problem
    By imranmd in forum Commercial
    Replies: 5
    Last Post: 07-03-2008, 06:13 AM
  4. Excessive Frosting on the Evaporator
    By vadivelan in forum Fundamentals
    Replies: 5
    Last Post: 23-06-2007, 12:18 PM
  5. Excessive Superheat
    By AEGIS Cool in forum Technical Discussions
    Replies: 13
    Last Post: 26-11-2006, 09:06 PM

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •