    Mitsy city multi help



    Hi fellas,
    I have a mitsubishi model PUHY-P200 YGM-A.(410 a)
    the compressor was replaced along with the inverter board and ipm board. ( not by me ). the job has been dumped on my lap and as Im more familiar with chillers a little guidance is needed (before i call the mitsy service boys in )
    i currently have a fault code 0403.
    all the connections on the inverter board seem ok as well as the main board.
    where to from here.

    REGARDS



  2. #2
    Join Date
    Dec 2008
    Location
    UK
    Posts
    564
    Rep Power
    24

    Re: Mitsy city multi help

    As you have eliminated the possibility of a bad connection between the INV board and the FAN board, you may need to check the inverter address switches are set correctly. Check the address of SW2-1 on INV board. Check SW2-1 on the FAN board whether it is ON. Possibility of transformer failure, measure the voltages between pins 1 and 3 of the FAN board connector CNTR. Or worse still you could have either a defective INV board or a defective FAN board. Check these items first.

  3. #3
    Join Date
    Mar 2007
    Location
    Warwickshire UK
    Posts
    723
    Rep Power
    21

    Re: Mitsy city multi help

    I would also be looking carefully at the power supply for correct 3ph voltage & no voltage on the N line.
    A power supply problem like floating N can cause inverter damage.
    So has the new inverter board / IPM also been dammaged ?

    If the old compressor & inverter parts are still available for inspection you could find out why these items were replaced.
    If the compressor windings are down to ground with a mega test then that would cause damage to the IPM & possible damage to the inverter board.

  4. #4
    Join Date
    Jul 2008
    Location
    australia
    Posts
    8
    Rep Power
    0

    Re: Mitsy city multi help

    thanks for that fellas
    you were correct it was the inverter address.
    I picked up the service manual today and i must say im keen to learn more about these machines.
    is there any other suggested reading or is it all on site learning.
    once again thanks and have a bonza christmas ,im off for a surf.

  5. #5
    Join Date
    Nov 2008
    Location
    UK
    Posts
    69
    Rep Power
    16

    Re: Mitsy city multi help

    Quote Originally Posted by philstead View Post
    once again thanks and have a bonza christmas ,im off for a surf.
    You rotten bugger! We've got 2 foot of snow here today

    Mitsi or their local distributors should have training courses (assuming it's the same as here)

Similar Threads

  1. mitsi city multi
    By transit 1 in forum Air Conditioning
    Replies: 2
    Last Post: 05-10-2008, 09:08 PM
  2. Mitsi City Multi 7100 code
    By lonemascot in forum Air Conditioning
    Replies: 4
    Last Post: 14-05-2008, 07:34 PM
  3. Commissioning City Multi
    By dallan in forum Air Conditioning
    Replies: 5
    Last Post: 22-09-2007, 09:39 PM
  4. Need input on City Multi
    By TDfromNY in forum Air Conditioning
    Replies: 4
    Last Post: 09-06-2006, 03:31 AM
  5. city multi
    By techni in forum Air Conditioning
    Replies: 1
    Last Post: 30-06-2002, 11:02 AM

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •