Heat load calculations Help!
Ok im having a few dramas calculating airchange load. Product load & defrost load. Here is what i have so far. Im calculating over 24 hours.
The room is loaded with 1500kg of product per day
The storage temp is -35
Temp of product entering the room is 35 degrees
The specific heat of the product above freezing is 3.182kj
The specific heat of the product below freezing is 1.717kj
The freezing temp is is -1.17
The latent heat of fusion is 233.48kj
there are 6 x 20 minute defrosts per day with the heater elements totaling 10Kw
Ineed to allow for 2 complete air changes
here is what i have so far
Airchange Load = IRVxACFxenergyxusage/time
IRV -LxWxH = 15x10x5 = 750m3
Now i have not been given an ACF(or is that 2^ )
Energy - 60%R.H, - 35 degrees storage =0.1045
Usage Factor - im assuming it is 1
1 hour = 3600 seconds x 24 = 86400 seconds
So i have gone :
IRVxACFxEnergyxUsage/time
750m3 x (2?) x 0.1045 x 1/86400= 1.814236111Kw
Now for defrost load
10Kw x 2/24=0.83Kw
Now for the product Load
Q=m x cp x deltaT
m=1500kg
cp=3.182 - Above freezing
1.717 - below freezing
delta T - 35+1.17=36.17 - Delta T above freezing
-35--1.17=33.83 Delta T below freezing
Pull down time 24hours =86400 seconds
so 1500kg x 3.182 x 36.17=172.639/86400=1.998Kw
1500kg x 1.717 x 33.83=87.129/86400=1.008Kw
1.998 + 1.008=3.006Kw
how do i work out the latent heat?
Thanks for your help here guys. I cant be to far off can i?
-
29-09-2009, 07:50 AM #2
Re: Heat load calculations Help!
anyone?
-
29-09-2009, 09:19 AM #3
-
29-09-2009, 09:28 AM #4
Re: Heat load calculations Help!
1500* 233= 359500Kj/3600=97Kwhrs
97/ 24=4.045Kw. plus all others.
But I would not use the total rating as the rating for your condensing unit.
(Total *24)/18 run hours.
Other issues that need to be considered is this just freezing product or is it also longer term storage.
You need to to size your condensor for a higher evap temp (SST) and/or install CPR.
There are also limits on the product
If it is one big lump then will not freeze in 24hrs, but if very small bit will freeze easy, raising room temp.
-
30-09-2009, 04:39 AM #5
-
17-10-2009, 07:34 AM #6
Re: Heat load calculations Help!
can anyone help me nail this one?
-
17-10-2009, 09:49 AM #7
Re: Heat load calculations Help!
Hi there,
Latent heat unit is kJ/kg NOT kJ.
So : m x LH /86400 = 1500 x 233.48 /86400 = 4.05 kW
What seems to be the problem?
CheersEven Einstein Asked Questions
-
17-10-2009, 11:12 AM #8
Re: Heat load calculations Help!
May be your are not understanding Kj/Kg this is energy, there is no time involved, so you have to work out total energy then divide by a time you want this to happen in. But you then have to include defrost and off times, which increases the refrigeration capacity over that of your original calculation
Similar Threads
-
Basics or is it?
By Fett in forum FundamentalsReplies: 17Last Post: 10-09-2009, 01:45 AM -
Heat Load Calculations
By tjk2007 in forum Tools and CalculatorsReplies: 7Last Post: 11-05-2008, 02:24 AM -
Compressor loading, cooling, and range of operation.
By Air duster in forum FundamentalsReplies: 10Last Post: 02-04-2008, 08:39 AM -
frostles heat pump
By Lc_shi in forum New TechnologiesReplies: 27Last Post: 31-03-2008, 07:53 AM -
Heat Load Calculations - Part L Building Regs
By Refrigerologist in forum Tools and CalculatorsReplies: 6Last Post: 12-03-2008, 09:53 AM