Results 1 to 8 of 8
    Dec 2008
    Brazil
    106
    10
    A/C Pressure problem - Low side too high
    The a/c system was evacuated and added R134
    Low pressure side 70PSI ( too high) and high pressure side 140PSI (too low)
    Can it be excessive refrigerant load ?
    Compressor is running all time (non-stop)
    Moises
    Mar 2008
    United Kingdom
    52
    11
    Re: A/C Pressure problem - Low side too high
    I assume your talking about car A/C and it sounds very much like your compressor is not pumping.......
    Split Croatia
    6,106
    7
    30
    Rise your engine RPM and then measure pressures!
    Mar 2008
    United Kingdom
    52
    11
    You have to take into consideration that he is in Brazil which is about 30C ambient, and with a suction pressure of 70 PSI I would expect a discharge pressure well in excess of 140 PSI.
    Aug 2009
    Turhona.libya
    72
    9
    If you are talking about car ac system i would say that if everything is normal the suction pressure should not exceed 35 psi in the start up and will get lower when the temp. Is getting down or the the speed of the compressor is getting high. The said pressure means that the compressor is not pumping.
    Dec 2008
    Brazil
    106
    10
    Yes, it`s aumotive system
    I contacted him now and he said when he turns the compressor off, the low side goes to
    about 150PSI and also high side 150PSI
    Sorry for inaccurate information, and thanks in advance for efforts. I am not specialist, just a mechatronics teacher trying to assist my student which is far away from me
    Split Croatia
    6,106
    7
    30
    Quote Originally Posted by Acrisoft View Post
    That is normal and it tell us that ambient temperature is 40C (105F) if you telling us absolute pressure or 44C (112F) if you giving us relative pressure.
    What pressure you are giving to us, relative (gauge with -15,4psig at low end) or absolute (gauge with 0 psia at low end)?
    Dec 2008
    Brazil
    106
    10
    Problem was really the compressor
    Temperature is 25C to 27C and pressure gaugue not sure. Maybe more common type
  1. Superheat and Subcooling
    By Chunk in forum Fundamentals
    Last Post: 15-01-2011, 01:24 AM
  2. need help! compressor kicking out on high pressure
    By SloFuse in forum Trouble Shooting
    Last Post: 19-08-2009, 04:46 PM
  3. Help to solve problem on York chiller
    By nassersh in forum Trouble Shooting
    Last Post: 03-06-2008, 08:38 PM
  4. Maytag side by side auto defrost problem
    By m0t in forum Domestic
    Last Post: 02-06-2008, 12:47 PM
  5. Interesting Problem
    By NH3LVR in forum Industrial Compressors
    Last Post: 12-08-2006, 10:27 PM