    pobbo's Avatar
    pobbo Guest
    carrier chiller hp problems
    G'day
    i have a carrier Chiller 30GB-210.940
    Unique No. 30GB.210 OOO571
    S/N 0697W09089
    Unit has had a History of tripping HP on 30+(c) days
    Pipework does not seem to distribute hot gas evenly and bottom horizontal coils do no work
    anyone else had a similar problem chiller is about 12 years old
    Aug 2007
    Sydney
    52
    1,083
    23
    Re: carrier chiller hp problems
    Hi pobbo
    Check the HP sensor callibration and superheat and subcooling - aim for about 10k subcooling. Also check comp current, ref charge, and obviosly condition of heat exchanger. If the heat exchanger is degraded reduce ref charge. Look for any modification on liquid line ie smaller drier fitted. Check the above with a good load.
    Somerset
    69
    4,697
    pobbo.
    Welcome, I cannot really add much to Tesla's excellent advice.
    Other than to ask what you mean by the following- "bottom horizontal coils do no work"
    Is it because the fin condition has deteriorated so that there is poor flow through them?
    Or they may be oil logged?
    Damaged?
    System overcharged?
    Put me out of my misery, what is wrong with them.
    If it is down to old age etc. I have resorted to the old lawn sprinkler trick!
    Mind we don't suffer from water shortages as much over here.
    Cheers Grizzly
  1. York Chiller problems
    By ingherrera in forum Commercial
    Last Post: 26-07-2011, 03:10 PM
  2. Replies: 12
    Last Post: 27-03-2011, 04:12 AM
  3. Carrier 30XA Liquid chiller Problems
    By Ed Burris in forum Commercial
    Last Post: 13-08-2010, 08:12 PM
  4. Carrier chiller basic board problem
    By noushad123 in forum Trouble Shooting
    Last Post: 17-06-2010, 06:55 AM
  5. Carrier Chiller Help
    By superswill in forum Trouble Shooting
    Last Post: 18-01-2007, 10:06 PM