18-03-2009, 01:36 PM #1
Check valve noise - heat-pump
Hi everyone,
We have a heat-pump with a Copeland zr scroll compressor, with a 1/2" flare Castel check valve installed in the discharge line.
The piping restrictions mean that the check valve lies on approximately 15 degree incline.
At high temp operation, it seems like the check valve may be vibrating. The line is sized at discharge nozzle diameter - too small, in my view. My thoughts are that there may be excessive gas velocity through the check valve.
It's not a serious noise, but enough of a rattle to bother my ear.
Could anyone shed light on what is going on. Thanks so much.
-
18-03-2009, 07:24 PM #2
Re: Check valve noise - heat-pump
Hi!
I know that Danfoss uses special check valves in discharge lines to avoid resonance problem:
"In refrigeration plants with compressors
connected in parallel, it is advantageous to use
NRVH, since the spring is stronger than the one
utilised in NRV. Also, resonance problems can be
avoided at partial load in the refrigerant plant."
Because the stronger is the spring the higher is system's resonance frequencies.Last edited by narkom; 18-03-2009 at 08:20 PM.
-
19-03-2009, 12:52 AM #3
Re: Check valve noise - heat-pump
Hi Narkom,
Thanks very much for your comment. This makes sense in terms of resonance. Using the stronger spring would make sense here.
I'll look into the Danfoss range & bring one in. Now that you mention the NRVH, I remember seeing that in their catalog.
Excellent - thanks again for your wise advice.
Similar Threads
-
New Heat Pump Forum
By Argus in forum Heat PumpsReplies: 17Last Post: 10-04-2010, 09:12 AM -
Air source heat pump modification
By rt29781 in forum Heat PumpsReplies: 4Last Post: 23-12-2008, 08:41 AM -
swimming pool heat pump
By Andy AC in forum The Trail of TearsReplies: 8Last Post: 26-08-2007, 04:02 PM -
Heat Pump Modification
By mallmk13 in forum Trouble ShootingReplies: 2Last Post: 28-06-2007, 09:46 PM -
Air conditioning maintenance procedure
By Andy T in forum Air ConditioningReplies: 12Last Post: 27-05-2006, 06:57 PM