Thread: sanyo vrf
    Feb 2007
    SIDE OF THE ROAD
    263
    12
    sanyo vrf
    hi
    have a vrf system that has a caution sign displaying on all controllers connected, is therea way of finding out whats wrong? suspect it might be short
    any ides philip
    Dec 2005
    Manchester England
    Re: sanyo vrf
    Unit has gone into auto backup mode. Inverter compressor has been disabled. Try resetting by isolating outdoor power. If problem persist, check inverter compressor and inverter.
    Mar 2008
    98
    11
    Re: sanyo vrf
    Quote Originally Posted by philjd26 View Post
    hi
    any ides philip
    In some situations, auto address may have not been completed. A caution icon will display on all controllers in this circumstance.
    Has this system ran in the past, or is a new start-up? You may want to dis-connect power both Indoor and Outdoor and re set the entire system. Once power has been applied ...try auto address again....allow LED 1 and 2 to go completely out. If they are both out and not flashing together....try running the system.
    Hope this helps,
    Husky
    Feb 2007
    SIDE OF THE ROAD
    263
    12
    Re: sanyo vrf
    hi still having no joy with this problem...i have 3x vrf connected in common, i check alarm outdoor leds,all leds off....
    i checked all inverters diodes, transistors and windings for balance... all seem good,
    any ideas ?/
    Apr 2006
    stafford
    36
    986
    14
    Re: sanyo vrf
    Quote Originally Posted by sigorst View Post
    read your PM's !!!!!
    Paul
    "KEEP IT COOL"
    Jul 2005
    Ireland
    164
    13
    Re: sanyo vrf
    HI Philjd,
    Swill is correct Inverter compressor has shut down for some reason
    Could be any of the following
    Faulty HIC PCB
    Loose conection on PCB or Compressor
    (we'll assume you have checked all the basics)
    Low on gas on full load compressor may overheat Discharge temp above 108-111 degrees C.
    Pumpdown due to an SVK connected to an indoor not opening.
    High pressure for same reason in heating
    possible faulty compressor.
    Many more reasons.
    It's easy enough to check all of the above by connecting a standard sanyo remote control to the outdoor unit on terminals 3and4 then entering the sensor check mode.
    It's possible to check all system temperatures, pressures
    and current sensors by doing this in real time.
    If you want a service manual drop me a PVT message with your email and I'll send one on to you.
    Apologies for the late reply been real busy here
    T
  1. Sanyo fault codes
    By Slim R410a in forum Air Conditioning
    Last Post: 03-11-2008, 08:02 PM
  2. Sanyo system needs supplemental heat
    By mchild in forum Air Conditioning
    Last Post: 29-11-2007, 02:50 PM
  3. fault on a sanyo unit
    By marc5180 in forum Air Conditioning
    Last Post: 18-08-2007, 11:04 PM
  4. Sanyo inverter split unit
    By cikku in forum Domestic
    Last Post: 22-05-2006, 06:07 PM
  5. Sanyo equipment
    By Karl Hofmann in forum Air Conditioning
    Last Post: 17-09-2004, 08:39 PM