    Re: Mitsubishi ecodan Heatpump Boiler

    I would say to all those considering ASHP for UK heating that they should serioulsy consider either the Hitachi Yutaki or the Sanyo CO2 Eco.

    Both these units have had extensive R & D and pose the most realistic threat to traditional heating sources (boilers).

    The Sanyo, in particular, is currently the only ASHP able to allow DHW storge at 65 C (using heatpump alone) at minus 20 C and has sufficient built in backup/redundancy heating in case everything turns to Rat S**T ! As it comes as a matched package, it's the one least likely to give aggro.

    You get what you pay for!!

  2. #2
    Join Date
    Oct 2008
    Location
    North East
    Posts
    1,050
    Rep Power
    19

    Re: Mitsubishi ecodan Heatpump Boiler

    Quote Originally Posted by airconwarehouse View Post
    I would say to all those considering ASHP for UK heating that they should serioulsy consider either the Hitachi Yutaki or the Sanyo CO2 Eco.

    Both these units have had extensive R & D and pose the most realistic threat to traditional heating sources (boilers).

    The Sanyo, in particular, is currently the only ASHP able to allow DHW storge at 65 C (using heatpump alone) at minus 20 C and has sufficient built in backup/redundancy heating in case everything turns to Rat S**T ! As it comes as a matched package, it's the one least likely to give aggro.

    You get what you pay for!!
    I would be keen on seeing some data tables and specs at the different temperatures to show the heat pump output?

    Can you provide a link?

  3. #3
    Join Date
    Aug 2008
    Location
    England
    Posts
    12
    Rep Power
    0

    Re: Mitsubishi ecodan Heatpump Boiler

    http
    :
    //
    eu.sanyo.com/
    AssetBrowser/
    Air%20Conditioning%20Docs/
    Brochures/
    SANYO_CO2_ECO_Heating_System_v1.pdf

    Note it is 3.6 Mb. See page 11.
    65degC output temp
    At +7 degC air temp the COP is 3.1
    At -15 degC air temp the COP is 1.8

    So maybe not as efficient as HFC above zero air temp, but producing 65 water output temp must affect it.

  4. #4
    Join Date
    Nov 2007
    Location
    London
    Posts
    461
    Rep Power
    17

    Re: Mitsubishi ecodan Heatpump Boiler

    Daikin Altherma have released a high temperature range which operates to temperatures of up to 80 degrees.
    The perfect solution for UK climates which most tech's will be able to work on which is a great solution by the looks of it.

  5. #5
    Join Date
    Mar 2009
    Location
    KZN, South Africa
    Age
    64
    Posts
    2,212
    Rep Power
    20

    Re: Mitsubishi ecodan Heatpump Boiler

    Quote Originally Posted by brunstar View Post
    Daikin Altherma have released a high temperature range which operates to temperatures of up to 80 degrees.
    The perfect solution for UK climates which most tech's will be able to work on which is a great solution by the looks of it.
    I would love to know what compressor model these are using.

    At a water delivery temp of 80'C, SCT must be >=~80'C, unless pulling a little more from the refrigerant superheat. Even then SCT must be at least 75'C.

    Wonder what lifetime testing these folks have to back up their claims. I'd be intrigued.

    Engineering Specialist - Cuprobraze, Nocolok, CD Technology
    Rarefied Technologies ( SE Asia )

  6. #6
    Join Date
    Apr 2001
    Location
    New Port Richey, Florida - USA
    Age
    79
    Posts
    5,071
    Rep Power
    35

    Re: Mitsubishi ecodan Heatpump Boiler

    Quote Originally Posted by desA View Post
    I would love to know what compressor model these are using.

    At a water delivery temp of 80'C, SCT must be >=~80'C, unless pulling a little more from the refrigerant superheat. Even then SCT must be at least 75'C.

    Wonder what lifetime testing these folks have to back up their claims. I'd be intrigued.

    From what little I have found online, it seems that Daikin builds their own compressors and if I am not mistaken, the Altherma uses an inverter driven model.

Similar Threads

  1. Mitsubishi vrv
    By dakesojo in forum Air Conditioning
    Replies: 20
    Last Post: 22-09-2009, 01:04 PM
  2. Replies: 6
    Last Post: 11-12-2007, 11:38 PM
  3. Mitsubishi Light Truck Refrigeration
    By Mastercool in forum Transport
    Replies: 2
    Last Post: 23-11-2007, 06:15 AM
  4. mitsubishi city multi fault code
    By robin r33 gtr in forum Air Conditioning
    Replies: 5
    Last Post: 05-11-2007, 10:23 PM
  5. Mitsubishi compressor lock
    By marc5180 in forum Air Conditioning
    Replies: 29
    Last Post: 08-10-2007, 05:48 PM

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •