Thread: R600a Repair Help
-
22-12-2007, 06:14 AM #1
R600a Repair Help
hi guys
I really need some info about R600 repairs and tools.
-
22-12-2007, 11:00 AM #2
Re: R600a Repair Help
No Not Yet.i Just Got Some Files Sent Over
-
22-12-2007, 06:06 PM #3
Re: R600a Repair Help
R600 is no more difficult or special than any other refrigerant.
Just bare in mind that it could go pop.
I bet you have been camping and have used a stove to cook food and boil water?
We are at less risk while using it as a refrigerant than you would be trying to light it to cook.
taz.
-
22-12-2007, 06:15 PM #4
Re: R600a Repair Help
Would that be a "flash in the pan" taz?
Interesting outlook, totally practical untill the H&S Brigade have a say!
Grizzly
-
29-03-2008, 12:01 AM #5
Re: R600a Repair Help
i can gt some inf. about 600a gas
1. molecular waight 58.12
2. boiling point -11.80
3. critical tem. 134.98
4. critical pressure .mpa 0.551
5. specific heat of liquid25 2.38
6. vaporization heat under bp 366.5
-
29-03-2008, 03:17 PM #6
Re: R600a Repair Help
R-600 works well for cascade cooling of the compressors and as a bridge for oil seperation, R-600a I do not know much about it first hand.
-
29-03-2008, 08:08 PM #7
Re: R600a Repair Help
Hi, Michae
If you want to repair fridge with R600 , refill with gas , replace compressors , etc , must have an electronic refrigerant charging meter , with +/- 2g precision , because R600 quantity inside refrigeration circuit is 20 to 50 grams. Like tools , must have an Vulkan Lokring tools with accesory ( go to lokringusa.com) .
If i do not have Lokring tools with me , I make so :
A - for refill with R600
1-OPEN THE WINDOWS OF THE ROOM , because R600 is FLAMABLE !
2- cut charging pipe of compressor to purge R600
3- connect vacuum pump in circuit , and start the compressor , to extract R600 from the oil.
4- after 10 min , stop the vacuum pump and check if vacuum in stable. I repet the procedure 2 or 3 time.
5-when i have vacuum inside , i conect with brazing an service port to charging pipe .
6 - i repeat vacuum procedure and charge the fridge with R600 like in technical instructions ( inside label with technical parameter )
B replace the compressor
Is the same , but i cut compressor pipe in this situation and i replace the filter dryer .
Atention: this is practical procedure only for extreme situations.
Similar Threads
-
R600a
By Andy W in forum DomesticReplies: 46Last Post: 27-09-2011, 08:14 PM -
R600a in USA residential refrigerators?
By robatalha in forum New TechnologiesReplies: 0Last Post: 24-10-2007, 03:55 AM -
Fittings for R600A
By Igor in forum HydrocarbonsReplies: 1Last Post: 23-09-2007, 11:28 PM -
R600a
By fireblade in forum RefrigerantsReplies: 12Last Post: 23-07-2006, 10:57 PM -
Repair of screws
By reggie in forum Industrial CompressorsReplies: 6Last Post: 04-08-2003, 05:26 PM