Re: all reefer container problems/daikin/carrier/thermoking/mitsubishi
Dear to all RE:
I need some advice because i will conduct a flashing. the unit is carrier although i have experience to do that but i want to have advice for some important to because the last compressor of that unit is broken so we buy a new compressor.
thank you and regards to all out there ^^
-
20-07-2011, 03:28 PM #3
Re: all reefer container problems/daikin/carrier/thermoking/mitsubishi
Hi Krish
Some times that s normal. But some times that s not normal. Yo have to check step by step below mationed;
* You have to do P-6 SMV test, pass or fail?
* You have to check refrigerant level in the system. Maybe refrigerant level is too much??
* You have to check TXV.
If all them ok below mationed no need repair to your unit...
Good luck.
see you
Reefer mechanic.
-
21-07-2011, 04:23 PM #4
Re: all reefer container problems/daikin/carrier/thermoking/mitsubishi
my dear friend,
thank you very much for the suggession. container is in transit and will do the test once it reach.
Thanks & Regards
Krish
Similar Threads
-
Container Reefer Unit for Controlled Atmosphere (CA)
By reeferman in forum New TechnologiesReplies: 9Last Post: 26-08-2011, 09:26 AM -
MICROPROCESSOR DIAGNOSTICS/Differnces beteween TK/CTC
By REEFER-TEK in forum TransportReplies: 12Last Post: 27-03-2011, 04:12 AM -
Help cutting open 40ft reefer, we now have problems
By adrian_uk17 in forum IndustrialReplies: 50Last Post: 28-11-2010, 08:11 AM -
Reefer container
By stevec in forum CommercialReplies: 2Last Post: 25-01-2009, 05:30 PM