    fdharmala's Avatar
    fdharmala Guest
    Unhappy Panasonic Inverter CU-S10JKP error kode H11. Help me..any body
    Some one can help me.? what is meaning error code H11 and how fixed the problem ?
    fdharmala's Avatar
    fdharmala Guest
    Re: Panasonic Inverter CU-S10JKP error kode H11. Help me..any body
    hello any body ?
    manchester
    5,639
    H11 Indoor / Outdoor abnormal communication
    > 1 min after starting
    operation
    Indoor fan operation
    only
    • Internal / external cable connections
    • Indoor / Outdoor PCB
    manchester
    5,639
    Troubleshooting
    When abnormality indication starts again
    Is there any wiring error?
    Correct the indoor-outdoor units
    connection wires
    Check the indoor-outdoor units’ connection wires.
    Disconnect terminal 3 wire and measure Vdc between terminal
    2 & 3 from the outdoor unit.
    Is the Vdc fluctuate between 20-70Vdc?
    Replace outdoor PCB
    Reconnect terminal 3 wire and measure Vdc between terminal
    Is the Vdc fluctuate between 20-50Vdc?
    Replace indoor unit PCB.
    manchester
    5,639
    emailed ya the manual- 7meg
    5,667
    Quote Originally Posted by fdharmala View Post
    hello any body ?
    Steady on there fella.....giving just 4 MINUTES before you start shouting for help is a little impatient
    We don't sit on here just waiting for questions you know
    manchester
    5,639
    took me 12 minutes to reply- and e mail manual,must be getting old
    also its been over an hour and no thanks,email reply - cant ask for rep points off a new member
    fdharmala's Avatar
    fdharmala Guest
    Wink Re: Panasonic Inverter CU-S10JKP error kode H11. Help me..any body
    Troubleshooting
    connection wires
    Replace outdoor PCB
    Ok thankyou very much for help me. i'll chek the PCB and if i have any problem i'll give news soon.
Tags for this Thread