    Re: The Mysteries of Ammonia!

    have not done that.

    but, my last ammonia leaking job along with local fire brigade was the most memorable one.

    the leak was during holidays in early feb 2007.
    as early as 0700hrs i have received call from GM of the company.
    by the time my technican arrive on site, keep-off lines have been put up. few fire engines has arrived on site.

    white smokes are coming from the leaking poins. it is a hi-lo stage liquid pumped system.

    accessibility was poor then plus others are not familiar with the place.

    however, the main valves and branch valves were isolated along with others equipment. [practically the whole area is shutdown]

    you know what ...
    when i went in with only full facial mask with K2 filter, i came out with my lower body feel burning hot.

    good experience then ... but scary ... the smokes looks as if you are in heaven ...
    Last edited by hendry; 04-01-2008 at 05:06 PM. Reason: remove sensitive words

Similar Threads

  1. contaminants in ammonia systems
    By Johnny Rod in forum Refrigerants
    Replies: 29
    Last Post: 17-10-2011, 05:26 PM
  2. Want to be trained as an ammonia operator
    By Randy Williams in forum NH3
    Replies: 7
    Last Post: 26-11-2008, 08:15 PM
  3. Replies: 21
    Last Post: 03-02-2008, 05:10 PM
  4. Ammonia and CO2 reactor
    By gwapa in forum NH3
    Replies: 18
    Last Post: 07-01-2007, 04:50 PM
  5. New Ammonia Certification in United States
    By JerrydNH3 in forum NH3
    Replies: 11
    Last Post: 15-08-2006, 03:10 PM

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •