23-03-2008, 02:33 PM #1
DAIKIN Drain Pump
Greetings all.
I am carrying out the installation of more than 300 indoor unit and it is very important to know if there is a check valve in the indoor units (with drain pump) or not?
-
23-03-2008, 11:01 PM #2
Re: DAIKIN Drain Pump
They do not normally have a check valve as far as I know.
The discharge pipe from the unit should ALWAYS fall towards a the drain outlet.
The pump is not designed to pump against a large head of water.Brian - Newton Abbot, Devon, UK
Retired March 2015
-
24-03-2008, 12:24 AM #3
Re: DAIKIN Drain Pump
I agree with Brian UK , no check valves even on the cassette model as that has a pump but only to lift 300mm then gravity must be involved from there to the outlet of the drain .
If I was putting in 300 of something I would be expecting an answer
from the supplier or Daikin
Last edited by Toolman; 24-03-2008 at 12:26 AM.
60% of the time it works everytime.
-
24-03-2008, 09:44 AM #4
Re: DAIKIN Drain Pump
There is some info here that might help, plus your local Daikin contact details etc.
http://www.daikinme.com/downloads/default.jsp
-
24-03-2008, 11:30 AM #5
-
24-03-2008, 01:38 PM #6
- Join Date
- Sep 2007
- Location
- Split Croatia
- Age
- 57
- Posts
- 6,151
- Blog Entries
- 6
- Rep Power
- 36
Re: DAIKIN Drain Pump
No it is not necessary to install check valve.
You need to lay condensation pipes in order that you ensure proper drain of water from them by gravitation.
That mean that condenser pump only lift water column to higher point (approximately 0,5 m is max, consult commissioning literature) immediately at location of indoor unit and from that point it should drain itself by gravitation to collection point or collection pipe who must be at lower point.
-
24-03-2008, 02:02 PM #7
Re: DAIKIN Drain Pump
When installing multiple drains and they 'tee' into drains from floor levels above, this can lead to a problem of water leaking from the fan coils on a lower level if a drain blocks elsewhere. Rare, but it does happen! I sometimes install a waterless trap HEPvO type into the condense drain if the indoor fan coil is located above sensitive equipment to prevent this from occuring. I always install this type of trap at the end of the condense drain before it enters a soil or rain water pipe.
Last edited by Refrigerologist; 24-03-2008 at 02:06 PM.
-
24-03-2008, 04:55 PM #8
-
24-03-2008, 05:07 PM #9
Re: DAIKIN Drain Pump
Can you run separate drains from each floor to get around that problem?
Brian - Newton Abbot, Devon, UK
Retired March 2015
-
24-03-2008, 05:19 PM #10
-
24-03-2008, 10:48 PM #11
Re: DAIKIN Drain Pump
Brian - Newton Abbot, Devon, UK
Retired March 2015
-
25-03-2008, 03:19 PM #12
-
25-03-2008, 04:14 PM #13
- Join Date
- Sep 2007
- Location
- Split Croatia
- Age
- 57
- Posts
- 6,151
- Blog Entries
- 6
- Rep Power
- 36
Re: DAIKIN Drain Pump
What kind of pipes you using for condensate drain?
I usulay using PP pipes for domestic waiste like this:
http://tinyurl.com/2xax6t
I usually starting with 32 mm diameters at Fan-coil and gradually raising diameter as number of connections raising (and for large AHUs) and applying same rules as plumbers for layout practice. No siphons and decline of 1% is mandatory. All branch connections to collector pipe must be from above. leak test at commissioning.
I don't have single case of pipe obstruction or leakage from day one of that practice (more then 10 years).
-
26-03-2008, 11:04 AM #14
Re: DAIKIN Drain Pump
I usually using PVC pipes starting with 25 or 32 and raising diameter as number of connections raising like u.
Our service area here about 50 cm from slap to false ceiling and we have a lot of works in this area I can't run separate drains from each unit.
-
26-03-2008, 12:45 PM #15
Re: DAIKIN Drain Pump
When I have done office installations etc. I generaly ran a couple of main drains in (depending on void depth v drain length v unit drain height (modified by pump head where fitted).
The drain preferabley copper would be trapped and air broken before joining main drain or other. Individual air breaks for each unit would be achieved by sizing for 15mm or 22mm (depending on unit requirements) draining into open connections on the main condensate drain. If you size the main drain correctly, keep it rigid enough and ensure a good fall (I would suggest no less than 1:40) then you will have no trouble plus its easy to add rodding points and you can intorduce biocide and stuff at any or all the air breaks.
-
26-03-2008, 07:57 PM #16
Re: DAIKIN Drain Pump
Generally all condensates are run in 32mm (11/4") pvc waste as per manufacturer's requirements, fall is minimum 1mm in 900mm.
The waterless trap solution will not cause you any problems elsewhere. If the main drain blocks then the water will back up in the pipe and find its way out of the lowest point, that is the lowest fan coil. Waterless traps can prevent this except for where a large column of water builds up in the main stack and reverses the bladder in the trap. But if the main stack blocks you would be in deep doodoo anyway!! Tundishes can be useful too, but you need to be careful, if a stack pipes back up. I have seen a couple of building flooded due to rain water pipes blocking and water pouring back out throught the tundish!
The main reason I use waterless traps is they do not dry out in the heating season, so we don't get foul odours coming out of the fan coils.Last edited by Refrigerologist; 26-03-2008 at 08:03 PM.
-
26-03-2008, 10:48 PM #17
Re: DAIKIN Drain Pump
Have you considered using a vacuum condensate removal system?
http://www.jetvac.ca/FAQ.htmBrian - Newton Abbot, Devon, UK
Retired March 2015
-
29-03-2008, 02:37 PM #18
Re: DAIKIN Drain Pump
Boget...Boget..!
-
29-03-2008, 11:49 PM #19
-
30-03-2008, 02:17 AM #20
Re: DAIKIN Drain Pump
Hi, Brian_UK
Originally Posted by 2007eng
http://www.urbandictionary.com/define.php?term=boget
Best regards, Josip
It's impossible to make anything foolproof because fools are so ingenious...
Don't ever underestimate the power of stupid people when they are in large groups.
Please, don't teach me how to be stupid....
No job is as important as to jeopardize the safety of you or those that you work with.
-
30-03-2008, 12:16 PM #21
Re: DAIKIN Drain Pump
Sorry I mean Budget.
-
30-03-2008, 09:19 PM #22
-
30-03-2008, 11:10 PM #23
-
03-04-2008, 01:54 PM #24
Similar Threads
-
liquid ammonia pump calvitation
By Kathleen in forum Trouble ShootingReplies: 23Last Post: 20-05-2011, 02:18 AM -
Daikin lift pump
By Slim R410a in forum Air ConditioningReplies: 10Last Post: 13-07-2009, 11:12 PM -
Help with condensor pump
By Bakerbj in forum Air ConditioningReplies: 23Last Post: 14-06-2009, 12:39 AM -
frostles heat pump
By Lc_shi in forum New TechnologiesReplies: 27Last Post: 31-03-2008, 07:53 AM -
SL/SB-400 Pump Down Procedures
By absolute-zero in forum TransportReplies: 1Last Post: 29-01-2008, 09:27 PM