    Re: earth leakage

    Quote Originally Posted by declan simmonds View Post
    hello all from my experince i have found out that tripping from rcd is caused by inbalance of live and neutral feed, its true you should supply each unit with a seperate rcd . Are the units inverter type ? as i have been told that you should change the rcd to a
    RCD TYPE D instead of a type B as it takes long to trip or maybe it allows for a great inbalance someone tell me if this is true or am i talking rubbish? as i have fitted a RCD D TYPE to my daikin multi inverter in my house, becuase before the compressor used to start up slowly and then ramped up and triped the type B breaker,
    now ive fitted the TYPE D it doesnt happen
    cheers declan
    Here in your statements you are mixing residual current protection device:
    http://en.wikipedia.org/wiki/Residual-current_device
    Type [AC or A or B]

    Standard IEC 60755 (General requirements for residual current operated protective devices) defines three types of RCD depending on the characteristics of the fault current.

    Type AC: RCD for which tripping is ensured for residual sinusoidal alternating currents.
    Type A: RCD for which tripping is ensured:
    • for residual sinusoidal alternating currents,
    • for residual pulsating direct currents,
    • for residual pulsating direct currents superimposed by a smooth direct current of 0.006 A, with or without phase-angle control, independent of the polarity.
    Type B: RCD for which tripping is ensured:
    • as for type A,
    • for residual sinusoidal currents up to 1000 Hz,
    • for residual sinusoidal currents superposed by a pure direct current,
    • for pulsating direct currents superposed by apure direct current,
    • for residual currents which may result from rectifying circuits, i.e.:
      • three pulse star connection or six pulse bridge connection,
      • two pulse bridge connection line-to-line with or without phase-angle monitoring, independently of the polarity.
    and miniature circuit breaker.
    http://en.wikipedia.org/wiki/Circuit_braker

    Type Instantaneous tripping current
    B above 3 In up to and including 5 In
    C above 5 In up to and including 10 In
    D above 10 In up to and including 20 In
    K above 8 In up to and including 12 In For the protection of loads that cause frequent short duration (approximately 400 ms to 2 s) current peaks in normal operation.
    Z above 2 In up to and including 3 In for periods in the order of tens of seconds. For the protection of loads such as semiconductor devices or measuring circuits using current transformers.
    Miniature circuit breaker should be of B type for inverters and for non inverters of C type
    Residual current devices should be of B type for inverters and A type for noninverters
    Last edited by nike123; 24-03-2008 at 09:48 AM.

Similar Threads

  1. Refrigerant Leakage
    By Pravin in forum Technical Discussions
    Replies: 11
    Last Post: 21-05-2006, 03:17 PM
  2. Earth faults
    By reggie in forum Technical Speculations
    Replies: 17
    Last Post: 28-01-2006, 06:22 PM
  3. Earth tapped transformers
    By phil68 in forum Fundamentals
    Replies: 6
    Last Post: 04-01-2006, 09:32 PM
  4. Earth continuity
    By bernard in forum Electrical
    Replies: 3
    Last Post: 04-04-2005, 06:35 PM

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •