Re: earth leakage
Here in your statements you are mixing residual current protection device:
http://en.wikipedia.org/wiki/Residual-current_device
Type [AC or A or B]
Standard IEC 60755 (General requirements for residual current operated protective devices) defines three types of RCD depending on the characteristics of the fault current.
Type AC: RCD for which tripping is ensured for residual sinusoidal alternating currents.
Type A: RCD for which tripping is ensured:- for residual sinusoidal alternating currents,
- for residual pulsating direct currents,
- for residual pulsating direct currents superimposed by a smooth direct current of 0.006 A, with or without phase-angle control, independent of the polarity.
- as for type A,
- for residual sinusoidal currents up to 1000 Hz,
- for residual sinusoidal currents superposed by a pure direct current,
- for pulsating direct currents superposed by apure direct current,
- for residual currents which may result from rectifying circuits, i.e.:
- three pulse star connection or six pulse bridge connection,
- two pulse bridge connection line-to-line with or without phase-angle monitoring, independently of the polarity.
http://en.wikipedia.org/wiki/Circuit_braker
Type Instantaneous tripping current
B above 3 In up to and including 5 In
C above 5 In up to and including 10 In
D above 10 In up to and including 20 In
K above 8 In up to and including 12 In For the protection of loads that cause frequent short duration (approximately 400 ms to 2 s) current peaks in normal operation.
Z above 2 In up to and including 3 In for periods in the order of tens of seconds. For the protection of loads such as semiconductor devices or measuring circuits using current transformers.
Residual current devices should be of B type for inverters and A type for noninvertersLast edited by nike123; 24-03-2008 at 09:48 AM.
Similar Threads
-
Refrigerant Leakage
By Pravin in forum Technical DiscussionsReplies: 11Last Post: 21-05-2006, 03:17 PM -
Earth faults
By reggie in forum Technical SpeculationsReplies: 17Last Post: 28-01-2006, 06:22 PM -
Earth tapped transformers
By phil68 in forum FundamentalsReplies: 6Last Post: 04-01-2006, 09:32 PM -
Earth continuity
By bernard in forum ElectricalReplies: 3Last Post: 04-04-2005, 06:35 PM