Panasonic system worked only 1.30 minute
Just have a quick test an old Panasonic
outdoor model CU-A182KR gas R-22.
The owner said the system just ran for 1 and half minute only. I asked him to tried to run the system 5 times and I touched the liquid pipe and gas pipe at the cool mode. Fan, compressor work at normal, but when the gas returned to the gas pipe and made a little thin ice cover the gas pipe, the system suddenly turned off by it self. I think with a reasonable condition the thin ice should be appeared at the liquid side instead of the gas side.
After tested 5 times,I asked him to changed to the heat mode, I just hear the little noise:"click" from one off relay,
waiting few minutes, the system can not start at the heat mode. Cameback to cool mode, it started at normal for 1 and minute again. Because I have'nt got the circuit diagram, so I just measured voltage, current, and I did not test the PSI with the gauge (just pass to the customer's house for 10 minute only in hurry), Anyone have any experience about this case? Please share to a young new air man. I was confused between electrical section and mechanic section.
If the fault from electrical section, then I should be needed circuit diagram as well.
Thanks for your time to read this case.
-
19-01-2008, 11:24 AM #2
Re: Panasonic system worked only 1.30 minute
Indoor fan running?
If the suction frosted up that's the only thing I could think of, sometimes the indoor fan motor and PCB dies on these. That's the only error I could think of that causes it to shut off so soon.
Thermistor or electronic error = shut of straight away or never start.
indoor fan motor = run for about 30 sec.
gas flow error = run until thermistor reaches cut off, ie more for than a few minutes the first time its switched on.Last edited by paul_h; 19-01-2008 at 11:27 AM.
-
19-01-2008, 12:53 PM #3
Re: Panasonic system worked only 1.30 minute
liqiud line frosting, looks like short of charge!
is the condensor being called for even though it is not running???
-
19-01-2008, 02:51 PM #4
Re: Panasonic system worked only 1.30 minute
do u have any error codes coming up anywhere??
my guess is its cutting out on LP (low pressure). an iced up suction line is generally a sign of a short of gas in the system.
-
19-01-2008, 03:22 PM #5
-
19-01-2008, 07:35 PM #6
Re: Panasonic system worked only 1.30 minute
If I only had ten minutes to check out a system and didn't have any tools with me, here's what I would check (and in this order):
Is the thermostat calling for cooling?
Is the evaporator fan running?
Is the evaporator coil clear?
Is the condenser fan running?
Is the condenser coil clear?
Is the compressor running?
Is the liquid line warm, but not hot?
Is the suction line cold, but not freezing?
At this point, I would have a pretty fair idea of what's wrong.
-
19-01-2008, 10:11 PM #7
Re: Panasonic system worked only 1.30 minute
unless it was a capilary tube system
-
20-01-2008, 12:28 AM #8
-
20-01-2008, 05:28 AM #9
Re: Panasonic system worked only 1.30 minute
-
21-01-2008, 07:33 AM #10
Re: Panasonic system worked only 1.30 minute
Dear Paul, yes I just rang to asked the customer, he confirmed that the fan indoor
didn't work. There was 2 stories house, last time I just went pass and didn't jumped to upstair, just the owner operated following my order only.
Thanks for your sharing the golden experiences.Best Regard.
-
21-01-2008, 02:34 PM #11
Similar Threads
-
Daikin fault codes
By Chris2005 in forum Air ConditioningReplies: 45Last Post: 21-03-2012, 10:09 PM -
System Burn Out Troubleshooting
By altaf22m in forum Technical DiscussionsReplies: 13Last Post: 07-05-2010, 09:24 AM -
Burn out System, Clean up procedure. & Troubleshooting.
By altaf22m in forum CommercialReplies: 19Last Post: 15-04-2008, 07:03 PM -
Fan model for system optimization
By autt in forum System OptimizationReplies: 8Last Post: 31-03-2007, 05:34 AM -
Refrigeration system proposal; comments please.
By DaBit in forum Technical SpeculationsReplies: 13Last Post: 01-01-2003, 03:42 PM