23-09-2007, 07:47 PM #1
alarm cancelation problem
Hello everyone I am new and I am asking for help.
I have 1997 GEA Grasso ammonia screw compressor and I can not cancel the high pressure discharge alarm.Every time I try, the screen says "alarm canceled" but the alarm comes back again and again.
-
23-09-2007, 08:21 PM #2
Re: alarm cancelation problem
Did you reset the high pressure pressostat?
-
23-09-2007, 10:59 PM #3
Re: alarm cancelation problem
I do not now haw to do it.
-
23-09-2007, 11:08 PM #4
-
24-09-2007, 09:32 PM #5
Re: alarm cancelation problem
If it's danfoss, screw the top of and reset is under the cover.
If it's any other brand, there should be a reset button somewhere under the cover, if not it's auto reset and either the pressure is still to high or the pressostat is broken!