cold room temp & the product temp
It is a well known fact that the cold rom temp is generaly the return air temp on the evap coil. many a times the client gets worried when the door is opened & the temp almost imediately shoots up. Though the product temp is unchanged, he is always worried.
Is there any technical literature explaining this phenomenon?
-
18-09-2007, 12:34 PM #2
Re: cold room temp & the product temp
The air temperature will always rise when a door is opened and external air is allowed inside.
The product temperature will remain more constant because of its mass.
Try changing the temperature probe from an 'air' sensor to a 'product' sensor or improve the the door seal arrangements to reduce the effect of door openings.Brian - Newton Abbot, Devon, UK
Retired March 2015
-
18-09-2007, 01:03 PM #3
Re: cold room temp & the product temp
Another option is to put the sensor for an elextronic thermometer in a 500ml bottle filled with glycol mixture (screwed to the wall).
When the customer looks at the thermometer, he will see the "mean" room temperature wich will be close to the temperature of the products in the room.
-
18-09-2007, 04:14 PM #4
Re: cold room temp & the product temp
Dear Viking,
Seems to be the practical suggestion. We can surely use that in our new projects.
-
18-09-2007, 05:42 PM #5
Re: cold room temp & the product temp
Hi
If its for future projects then look at your choice of controller.You could opt for a controller that controls the temp on return air but displays a % off Air on /Air off giving a more stable display temp.Or leave the the digital display inside the the controll panel and fit a box guage.
However if the customer is leaving the door open to long then your just masking the problem,it might be better to fit an annoying door alarm that activates after 60 secs.They,ll soon close the door.
Regards Bernard
-
20-09-2007, 03:22 PM #6
Re: cold room temp & the product temp
thats a good idea,
-
20-09-2007, 05:52 PM #7
Re: cold room temp & the product temp
or put a micro switch on the door so it stops the fans and pumps the unit down,with the probes being on or arround the blower they should stop stable untill the door is closed,but then they should expect it to go up a bit. this helps with icing up problems on freezers but if its a chiller i would go with the slow acting probe or the vessel with fluid in.
-
21-09-2007, 05:50 AM #8
Re: cold room temp & the product temp
Hi smpsmp45.
If you can check out ASHRAE Refrigeration Hand Book Chapter 12 " Infiltration Air Loads" , gives a good insight in to the effect of Warm Air flowing in to Freezer rooms. Frost accumulation and the formation of ice crystals can be a more adverse effect that product temperature rise.
-
21-09-2007, 07:59 AM #9
Re: cold room temp & the product temp
Dear John,
Many thanks
-
21-09-2007, 11:46 PM #10
Re: cold room temp & the product temp
Hi smpsmp45
The room tempertaure is formed for a 3D set of isotermal curves . The lowest temperature is leaving the evaporator and the highest is in the return (inlet of the evaporator). When you open a door this pattern changes and the highest temperature could be close to the door. A new isotermal pattern is formed. Normally the product has an inertial temperature constant that depend of many factor incluiding the enclousure. So the poduct do not react so fast to the temperature changes.It is a logarism aproch
If you instal a electronic temperatur sensor far from the door and in the return side of the farer evaporator It may help to have a better idea of the temperature.
You also could install hawain plastic courtain or even fast acting door together with horizontal openning door see www.ritehite.com
Similar Threads
-
Cold Room Design - minus 25deg C
By vijay_study in forum FundamentalsReplies: 34Last Post: 11-11-2009, 07:12 AM -
Compressor loading, cooling, and range of operation.
By Air duster in forum FundamentalsReplies: 10Last Post: 02-04-2008, 08:39 AM -
Compressor suction icing up on cold room set up
By Leviathan in forum Trouble ShootingReplies: 9Last Post: 02-06-2007, 05:08 AM -
LG Capacitor - Room not cold
By kelamel in forum Trouble ShootingReplies: 8Last Post: 21-10-2006, 10:50 AM -
Installation of cold room
By Josip in forum Legal-Business-MarketingReplies: 12Last Post: 12-03-2006, 09:20 PM