    Hello, has anyone had this experiance.

    A Unico System with a Highcool Heat pump.

    Problem! All wires from hard wired control panel via unico unit disconnected at outdoor unit, so, no communication from indoor to outdoor so it should be switched off.

    But, outdoor continues to run???? from approx. 42psi on Suction side until the pressure drops to approx 17psi then the compressor cuts out pressure slowly rises, compressor starts.
    This continues none stop.
    Has anyone experianced anything like this??????



  2. #2
    Brian_UK's Avatar
    Brian_UK is offline Moderator I am starting to push the Mods: of RE Site Moderator : and general nice guy
    Join Date
    Mar 2001
    Location
    Dorset
    Age
    76
    Posts
    11,024
    Rep Power
    60

    Re: Unico system

    Errr, seems like LP switch is working then.
    Brian - Newton Abbot, Devon, UK
    Retired March 2015

  3. #3
    Join Date
    Nov 2005
    Location
    Southampton
    Age
    46
    Posts
    54
    Rep Power
    19

    Re: Unico system

    Unico controllers usually work on 24v signal - is this compatible with youre hi cool unit??

    without the unico fan running the system will produce low pressure symptoms

    does the system have a pump down solenoid is it letting by??
    what size expansion valve have you fitted to unico coil (or is it a chilled water version)
    has the system been commissioned properly??

  4. #4
    Join Date
    Jul 2007
    Location
    staffordshire
    Posts
    22
    Rep Power
    0

    Re: Unico system

    This system works in cooling and heating modes, it just continues to operate after you switch the system off

  5. #5
    Join Date
    Mar 2006
    Location
    Lancashire
    Posts
    1,859
    Rep Power
    28

    Re: Unico system

    Glad its not just me then, that comes across units with strange faults

Similar Threads

  1. Daikin fault codes
    By Chris2005 in forum Air Conditioning
    Replies: 45
    Last Post: 21-03-2012, 10:09 PM
  2. System Burn Out Troubleshooting
    By altaf22m in forum Technical Discussions
    Replies: 13
    Last Post: 07-05-2010, 09:24 AM
  3. Replies: 19
    Last Post: 15-04-2008, 07:03 PM
  4. Fan model for system optimization
    By autt in forum System Optimization
    Replies: 8
    Last Post: 31-03-2007, 05:34 AM
  5. Refrigeration system proposal; comments please.
    By DaBit in forum Technical Speculations
    Replies: 13
    Last Post: 01-01-2003, 03:42 PM

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •