    Oil return PHE
    We have some unused R 12 units (compressor / condenser). We need to cool water down. Therefore, I thought that I could change the units to f. example R 413 and buy a plate heat exchanger. Then a friend tells me that I will get a problem with return of oil, as the new refrigerants are not working so well with plate heat exchangers. As my practical experience with these new refrigerants (and *****) is limited, I would like a comment on that.
    Is that so? If so, why is that so?
    Saludos
    Pobody
    Jun 2001
    N.Ireland
    1,630
    Hi,pobodyNerfect
    could you not pick an easier name to spell
    I would doubt if you would have oil return problems, provided you use an R12 drop-in.
    The reason for poor oil return may be due to retrofits, where the gas was dropped into a pre-existing system. If you TEV and pipework are selected as good design predicts, why would it not work, there is nothing magical about the drop-ins they are just R12 replacements which to all intense purposes work like R12.
    PHE to my experience are good at returning oil partially due to the rapid boiling action which ensues in the small heatexchanger internal surface area (relative to say a shell and Tube heat ex)
    Regards. Andy.
    Jan 2003
    Venezuela
    58
    22
    Thank you, Andy,
    Well, I have asked for a quote from a PHE manufacturer and will se what they come up with.
    Thanks again.
    P
    I shall consider your request
  1. pressure drop of pump return line ammonia
    By Moeller in forum Fundamentals
    Last Post: 04-09-2007, 05:21 AM
  2. Refrigeration Cases and Return Air
    By Capt Steve in forum Supermarket Refrigeration
    Last Post: 10-02-2005, 07:02 AM
  3. Oil return problems
    By Peter_1 in forum Industrial
    Last Post: 23-08-2004, 11:30 PM
  4. R404a Oil Return
    By dallan in forum Industrial
    Last Post: 23-08-2004, 12:40 AM
  5. return air
    By subzero*psia in forum Air Conditioning
    Last Post: 12-07-2001, 04:02 PM