Thread: change *****
    Nov 2005
    Moscow
    change *****
    Hi to all
    I am very intresting
    What if chiller with scroll compressor ( oil synthetics)lose its R407c ***** -
    Possible charge it R22 after repair?
    thanks
    Sep 2006
    Londrina
    Re: change *****
    Hi, End better to consult the manufacturer of the equipment, poid will be able to have problems.
    Mauro
    Jul 2006
    Israel
    70
    12
    Re: change *****
    Worst case scenario you should do a deep evacuation of the system , maybe change oil and oil filter ( with the original synthetic oil and original oil filter) and it should work.
    The pressures and temperatures of both gases are very similar , so it should work . all the best , Tzvi.
    Oct 2003
    5,630
    Re: change *****
    Rfcont, why not use R407c if that was the original refrigerant?
    Why you want to change it to R22?
    Nov 2005
    Moscow
    Re: change *****
    The problem itself interesting
    Transition from ***** R22 on R407c known as retrofit is in detail described in the literature and I would like to know return process just in any case
    (besides R407c rather expensive stuff)
    Sep 2005
    uk
    499
    Re: change *****
    Heard recently about a split a/c unit on r22, usual story, short of gas and fried compressor. changed r22 pot for r407 pot as all that was available at the time. charged r22, runs fine. how long will it last? who knows? but i suspect r22 will move synthetic oil around the system as happily as r407.