    Carrier Conversions
    I've been asked to convert 3 x 70kw Carrier air cooled DX condensing units from R22 in preparation for the phase out of R22.
    The units are single stage 6 cylinder semi - hermetic compressors (76A flc) with no unloaders. They appear to be recon compressors and operating quite satisfactorily.
    Which gas should I choose?
    It's an air conditioning application presently evaporating at 5C.
    Re: Carrier Conversions
    A little bit here Frank by someone else regarding a chiller gas change might be of interest.
    http://www.modbs.co.uk/news/fullstor...ler_life_.html
    plus this item from earlier...
    http://www.refrigeration-engineer.co...hp/t-1727.html
    5,667
    Thanks Brian - I was considering R59 but I've heard bad reports of oil recovery.
    Dec 2005
    Zagreb
    190
    Thumbs up Re: Carrier Conversions
    R407c and you can keep TEV.
    Renato
    5,667
    Quote Originally Posted by Renato RR
    Renato
    There may be a residual oil problem with 407C
    Dec 2005
    Zagreb
    190
    Well you will nedd change it 4-5 times before becomes ok.Cut off all sifons and empty old oil from traps.
    Renato
    Jun 2001
    N.Ireland
    1,630
    Quote Originally Posted by frank
    In a case such as this a phased change is better. First change the oil to ester oil, keep the R22 and keep changing the oil until the lab tells you the mineral oil % is below 1 to 3% (your oil manufacturer will help you with this figure).
    When the oil is flushed, then it is time to change to the new refrigerant, probably R407c, even though I don't like it, it is probably the only alternative atthe moment.
    Hope this helps.
    Kind Regards Andy
    Mar 2006
    Philippines
    124
    I used r407c for replacement of r22. No problem yet.
    Feb 2006
    Conversion from R22 to a HFC such as R407c is frought with problems, and could be a very costly exercise.
    Du Pont now offer the Isceon range and we have found Isceon 59 (R417a) excellent as a 'Drop In for R22 on DX systems.
    This gas is not cheap and the recommendations by DU Pont to thoroughly leak test must be followed.
    You may also have to adjust the TEVv and should use tables for R417a to check superheat & subcooling levels. Sometimes the cage / orifice size may need to be increased.
    5,667
    After studying various reports I chose to convert with R417a. One unit has been sucessfully converted with excellant results but I'm waiting on Carrier to provide further gaskets etc (due in from the States soon I'm told) before I can proceed with the other 2.
    http://www.eurocooling.com/articlerhodia.htm
  1. carrier fault codes
    By richelli in forum Trouble Shooting
    Last Post: 18-06-2010, 07:35 AM
  2. Carrier chiller oil migration
    By lowtech in forum Industrial
    Last Post: 30-04-2006, 04:11 PM
  3. carrier remote
    By superswill in forum Trouble Shooting
    Last Post: 26-04-2006, 09:17 PM
  4. Carrier spares
    By daddymac in forum Air Conditioning
    Last Post: 21-03-2006, 08:54 AM
  5. Required Control Wiring 50dp-020-910 Carrier
    By altaf22m in forum Air Conditioning
    Last Post: 08-08-2005, 06:08 PM