12-05-2006, 09:32 AM #1
Propylene System
Dear all,I have designed the R290 system,but I know few things about R1270(propylene) system? Who can help me?things about all parts of the system?
Thanks a lot.
sagittarius
-
12-05-2006, 02:15 PM #2
Re: Propylene System
Hi sagittarius,
The same principles apply to propylene also. You can use similar equipment for this refrigerant as the propane system you designed before.
As with propane, propylene has some strict requirements for the oil used. Otherwise, the dilution of the oil can cause severe problems with oil viscosity.
-
12-05-2006, 02:16 PM #3
Re: Propylene System
Yes, I confirm. Propylene and propane are more or less equivalent, and same requirements apply.
-
12-05-2006, 05:54 PM #4
Re: Propylene System
Hello,
check here about physical properties of gases, seems they are very close, check about oil:
http://www.praxair.com/praxair.nsf/A...25706F005926B7
Best regards,
Josip
It's impossible to make anything foolproof because fools are so ingenious...
Don't ever underestimate the power of stupid people when they are in large groups.
Please, don't teach me how to be stupid....
No job is as important as to jeopardize the safety of you or those that you work with.
-
13-05-2006, 01:10 AM #5
Re: Propylene System
Thanks all,I am very glad to read the answers on this sunny morning.Thanks.
But in the system,I don't know if the dry-filter is necessary?In the propane system I don't use this part,I think it is not necessary,but I am wondering that water in the system of propane or propylene will be frozen, won't it?Is it necessary other parts as simillar with R22?
-
13-05-2006, 01:17 AM #6
Re: Propylene System
If the system:
a) is properly leak tested and evacuated to provide a dry system, and
b) refrigerant grade purity is used you should be OK.
However, I believe you are right. Propane or propylene can carry water.
I never used any refrigerant driers on any of the hydrocarbon systems I designed though. But... We always supplied commissioning sheets stating the evacuation was required.
-
13-05-2006, 10:09 AM #7
Re: Propylene System
I'm afraid of the ice forming in the throttle.About the oil,I select the special oil for R290 or R1270 of CPI.(company from USA)
-
13-05-2006, 02:19 PM #8
Re: Propylene System
Propane you shall use is refrigeration grade. Not LPG from the fuel station.
-
13-05-2006, 03:10 PM #9
Re: Propylene System
If you are using the oil from CPI you are in good shape. This is the same company I used in the past with good success.
I would recommend them for other refrigerants too.
-
13-05-2006, 04:22 PM #10
Re: Propylene System
Hi, sagittarius
You did not explain what kind of plant is this one with propylene. Are you use it like refrigerant ( , maybe you are looking to retrofit R22) or that is a process plant where you have to extract (and maybe to liquify) propylene.
My friend was working in Russia and in Thiland at petrochemical plants using propylene as refrigerant (Stal screw S57) with some BP fully sintetic oil.
I was working here in one company on process plant with 3 stage reciprocating compressors (Sulzer-Burckhardt Swiss) to extract hydrogen (for butter production) at atmospheric pressure after electrolysis and storage into hp gas tanks (27 bar). We faced some problems regarding water which came from washing unit for electrolyte removal. Unit was equipped with condensing pots but from time to time we have to open piston heads and clean suction and pressure valves. There was not any problem with oil, it was the same type we use for air compressors.
Definitely you have to speak with compressor's manufacturer about oil.
Hope this can help a little.
Best regards,
Josip
It's impossible to make anything foolproof because fools are so ingenious...
Don't ever underestimate the power of stupid people when they are in large groups.
Please, don't teach me how to be stupid....
No job is as important as to jeopardize the safety of you or those that you work with.
-
13-05-2006, 04:50 PM #11
Re: Propylene System
Here is a set of Pressure/temperature curves for R-290, R-1270, & R-22 for others who are new to the use of hydrocarbons as refrigerants.
As you can see, R-22 is very similar to propane and propylene. Although propylene does have a somewhat higher pressure than the other two refrigerants.
This could be helpful at low temperatures to maintain a positive pressure in the evaporators. However, you also need to check the required mass flow and volume flow for the desired cooling capacity to see the impact of the refrigerant selected for the system.
-
13-05-2006, 04:56 PM #12
Re: Propylene System
I wonder what will happen if both refrigerants can carry water in a solution and where the temeprature drops in a small orifice?
It's better to keep your mouth shut and give the impression that you're stupid than to open it and remove all doubt.
-
13-05-2006, 11:02 PM #13
Re: Propylene System
Peter, you are correct. If water was present, ice would form at the expansion device if the outlet pressure was below the equivalent of 0C.
I wish I knew the right answer to this question, but I am not sure of the water solubility with hydrocarbons.
Perhaps Johnny Rod can answer this puzzle?
-
14-05-2006, 03:30 AM #14
Re: Propylene System
The R1270 system I'm designing is used for the ethylene cracking gas separation process plant.R1270 used as refrigerant.As same as
My friend was working in Russia and in Thiland at petrochemical plants using propylene as refrigerant (Stal screw S57) with some BP fully sintetic oil.
Thank you,Josip.I know the material compatibility for R290 and R1270 etc.The files is very useful for me.I have selected the Buna-N for R290,it is not suit for R1270.From the sheet only Viton can be selected.Not same as R22 used,is it?
-
14-05-2006, 03:41 AM #15
Re: Propylene System
Besides the above puzzle, I have the same thinking to the ammonia system.The present water in the R717 system maybe cause the same trouble,don't it?But in the R717 system there isn't filter-dryer.What happend?
solubility of water with refrigerants?
-
14-05-2006, 06:56 PM #16
Re: Propylene System
Originally Posted by sagittarius
Driers are available for ammonia, but not normally used.
-
14-05-2006, 09:52 PM #17
Re: Propylene System
Hi, sagittarius
Originally Posted by sagittarius
Originally Posted by sagittarius
But I think the same as NoNickName, what is normal. No need to use sh't and after to cry
Originally Posted by NoNickName
Best regards,
Josip
It's impossible to make anything foolproof because fools are so ingenious...
Don't ever underestimate the power of stupid people when they are in large groups.
Please, don't teach me how to be stupid....
No job is as important as to jeopardize the safety of you or those that you work with.
-
17-05-2006, 07:42 AM #18
Re: Propylene System
Tell me more special things,those should be paid attention to during desinging and running the propylene system?
-
18-05-2006, 08:10 PM #19
Re: Propylene System
Hi, sagittarius
Originally Posted by sagittarius
Best regards,
Josip
It's impossible to make anything foolproof because fools are so ingenious...
Don't ever underestimate the power of stupid people when they are in large groups.
Please, don't teach me how to be stupid....
No job is as important as to jeopardize the safety of you or those that you work with.
-
18-05-2006, 10:16 PM #20
Re: Propylene System
I'm also interested in designing systems with R290, but sources of components are scarce. Where do I find common refrigeration components suitable for R290. My usual suppliers are not of any help, or don't care at best.
-
18-05-2006, 11:49 PM #21
Re: Propylene System
Hi NoNickName,
What are you looking for? Any electrical component would of course have to be intrinsically safe for the area classification.
If it is for pressure regulators, etc. with non-electrical devices that is a different story.
Let me know what your requirements are and maybe I can find some information for you.
-
19-05-2006, 12:16 AM #22
Re: Propylene System
Hi,
regarding execution of unit working with R290, it must be equipped with electronical and electrical devices in explosion proof housing i.e. for petrochemical standards.
Recently we made one installation in one similar factory here and all protection was designed by engineers from that company (production of ammonia and fertilizers).
Unbeliveable story until we came to the end but we must follow the rules, no other way.
Best regards,
Josip
It's impossible to make anything foolproof because fools are so ingenious...
Don't ever underestimate the power of stupid people when they are in large groups.
Please, don't teach me how to be stupid....
No job is as important as to jeopardize the safety of you or those that you work with.
-
19-05-2006, 03:20 AM #23
Re: Propylene System
Originally Posted by josip
The purging was done with nitrogen and contained a differential pressure switch that maintained the control box at a slight positive pressure to resist the entrance of flammable vapors.
All conduits were run in heavy wall conduit, not the thin wall stuff. The conduits at the control box had what we called "pour off's".
The pour off's were a solid seal after the wires had be pulled and checked. This provided a vapor tight seal in the conduit and also prevented the entrance of flammable vapors and contained the purge.
All other electrical devices were constructed for the atmosphere just like any other conduit fitting for this area classification.
None of this is cheap!!! And I agree with josip... the standards used on this are VERY strict.
-
19-05-2006, 07:25 AM #24
Re: Propylene System
Electrical and electronic components are non-issue. I can find them.
The problem is with the refrigeration components, like TXV, solenoid valves, filters, etc. certified in group G1 of PED directive.
Thanks for your offer US Iceman.
-
19-05-2006, 09:29 AM #25
Re: Propylene System
Hi, NoNickName
Couple of months before I got request to find some manufacturers dealing with explosion proof A/C units for one petrochemical company.
Here are some links I found:
http://www.marcclimatic.com/products/splitsystems.htm
http://brooklynsevere.com/
http://www.iscsales.com/products/AC/...ion_proof.html
http://www.severeduty.com/catalog.html
http://www.explosionproof.net/window.html
http://www.nsls.bnl.gov/newsroom/pub...PRM-1.2.0.html
Hope this is of some help,
Best regards,
Josip
It's impossible to make anything foolproof because fools are so ingenious...
Don't ever underestimate the power of stupid people when they are in large groups.
Please, don't teach me how to be stupid....
No job is as important as to jeopardize the safety of you or those that you work with.
-
19-05-2006, 09:57 AM #26
Re: Propylene System
Thanks Josip, but we are producers, not resellers, so I'm interested in sources of components, not in equipment.
-
19-05-2006, 12:35 PM #27
Re: Propylene System
Hi, NoNickName
Originally Posted by NoNickName
I must admit that field is not my playground. I was working in such places but playing only with compressor (start up, adjustments) nothing related with explosion proof execution of units.
My working area is mostly in normal installation surroundings without explosion proof requirements.
Best regards,
Josip
It's impossible to make anything foolproof because fools are so ingenious...
Don't ever underestimate the power of stupid people when they are in large groups.
Please, don't teach me how to be stupid....
No job is as important as to jeopardize the safety of you or those that you work with.
-
19-05-2006, 12:54 PM #28
Re: Propylene System
I don't even need explosion proof components. Those are easy to find, and not even always required. For example fans do not need to be explosion proof, for air cooled chillers, because the 20% of LFL (lower flammability limit), will never be reached in open space.
I just need PED G1 certified refrigeration components.
-
19-05-2006, 02:31 PM #29
Re: Propylene System
Originally Posted by NoNickName
I don't know if Danfoss is one of your regular suppliers, but they have all kind of components for hydrocarbons (R600, R600a, R290, R1270 and R170):
thermostatic expansion valves TUBE, TCBE and TRE
solenoid valves EVRE
pressure switches KPE, MPE
check valves NRVE, NRVHE
sight glass SGIE, SGNE
filter driers DCLE
pressure transmitters MBS
....etc
-
19-05-2006, 03:54 PM #30
Re: Propylene System
I have a friend who's a teacher HVAC/R and he once converted a set-up to R-290.
He said that the properties were similar to those of the old R12, so very similar to R134a.
In the beginning days of R134a, we used our old R12 TEV's for R134a installations and this worked fine.
We once had an eutectic plate who failed. We had a small leak at the place where the tube entered the plate and teh plate was blown doubel it's size due to the expanduing refrigerant in the plate.
The plate was removed and they wanted to know where the leak was. They opened it with a grinder and as soon they went through the plate, it exploded. The person who did this had to be carried to the hospital.
What happened: the client had a leak and to save costs, a DIY he knew had add gass in it several months before. He added propane in it and this worked fine.It's better to keep your mouth shut and give the impression that you're stupid than to open it and remove all doubt.
-
19-05-2006, 04:11 PM #31
Re: Propylene System
Originally Posted by BESC5240
Thanks for the heads up.
-
23-05-2006, 10:40 AM #32
Re: Propylene System
Thanks all,I am absent to deal with many things recently.
Back here today,it's so many persons with me,it's my pleasure.
I am just same as NoNickName ,maybe.I want to find some auxiliary parts for my designing R290 ro R1270 system.The products of Danfoss titled above maybe don't provide in China.Maybe some of products did so.(US Iceman knew this matter.Thank you US Iceman ,I have selected the Magnatrol Float Level Controler.refer to thread "some questions of the Propane system")
For R290 system,I used the Hansen's products(solenoid valve,stop valve,filter,regulator valve,etc.) at last.There is a qustion with the valve provider,that is the capacity of refrigeration system.Sometime they can't provide the heavy duty valve.
-
23-05-2006, 10:46 AM #33
Re: Propylene System
Hi,Josip.The material of seal parts, such as O ring, gasket,is relation to only with oil?But the data from praxair ,different elastomers with the refrigerants.What's the matter?
-
23-05-2006, 12:12 PM #34
Re: Propylene System
Hi, sagittarius
Originally Posted by sagittarius
We have to check compatibility of our O-ring or gasket material in more ways; first with gas we intend to use (propylene), then with oils we can use with our gas (mineral, sintetic) and then with working conditions (high-low temp, high-low press) to check the strenght under different temperatures and pressures.
Sometimes you can not use any soft gasket for flange connection just metal to metal (conical shape) flanges.
Maybe you are worrying too much if you want to design your project using propylene you should get approval from compressor manufacturer for compressor and from other manufacturers for other parts. I think the best way is to request an offer according to your needs.
But...if you are going to make design, construction and manufacturing by yourself that is another story, you must start from begining, welcome to the nowhere
Please check here something more about:
http://o-ring.info/en/home/
and then on the same page go to basic elastomers
http://o-ring.info/en/basic-elastomers/
http://o-ring.info/downloads/en/tech...20Overview.pdf
http://o-ring.info/downloads/en/tech...l%20Tables.pdf
or here
http://www.dupontelastomers.com/Prod...rez/kalrez.asp
Hope this will help a little,
Best regards,
JosipLast edited by Josip; 23-05-2006 at 12:20 PM. Reason: adding link
It's impossible to make anything foolproof because fools are so ingenious...
Don't ever underestimate the power of stupid people when they are in large groups.
Please, don't teach me how to be stupid....
No job is as important as to jeopardize the safety of you or those that you work with.
-
23-05-2006, 05:27 PM #35
Re: Propylene System
That is good advice Josip.
Especially this:
But...if you are going to make design, construction and manufacturing by yourself that is another story, you must start from beginning, welcome to the nowhere
Great links posted by Josip.
-
24-05-2006, 01:23 AM #36
Re: Propylene System
Yes,that my job.But I am lack of experience in this region,I graduate from the major of refrigeration.I will do my best to reserch and designing.
I admire your self-giving spirits.This is a total sharing forum.
Thanks all,thanks RE.
sagittarius
-
02-10-2006, 08:22 PM #37
Re: Propylene System
Hi all
in denmark,a new law efected at jan 2007,says no more than 10kg. chage HFC pr. unit, (CFC, HCFC is not legal) so, Some companis have standart HC Chillers in ther product program, See Bundgaard Koleteknik Using R290 range 50-300kw or York koleteknikes Bonus unit using R1270 all PED-standart (en-378).
-
03-10-2006, 01:21 AM #38
Re: Propylene System
Hi kasperDK,
What refrigerant are they using when the capacity requirement is greater than 300 kW? Multiple units of smaller capacity???
Thanks.
Best Regards,
US Iceman
-
03-10-2006, 08:35 AM #39
Re: Propylene System
We use ammonia or multiple units ,normaly we say above 160kw R717 is more economic to builde/run this is for chillers 6/12 gr C,
for special low temp applications, we use (world lagest -55 gr Rum) think it is R170 ethan or R1150 ethylen , we use to use R23 for this application.
-
10-10-2006, 03:28 AM #40
Re: Propylene System
Just as a point of reference, we regularly build hc (hydrocarbon) based refrigeration sytems using recips, screws and centrifugal compressors. We address the electrical requirement of the U.S. as well as Europe, China and UAE.
We have another division that deals with XP (explosion proof) air conditioning units for off shore/marine applications.
It can easily be done, but it is not cheap.
Ken
-
16-01-2007, 09:19 AM #41
Re: Propylene System
Hi, I am missing for a long time.
I remember this home wherever and whenever.
In China, propylene refrigeration systems are used mostly in Petro and Chemical Industry .
-
22-01-2007, 03:55 AM #42
Re: Propylene System
Yes, water can be a problem in hydrocarbon systems. I would never operate a hydrocarbon system in a vacuum.
The water will remain free and will show up in two places. One is the compressor oil which will give you an apparent plugged oil filter as the paper fibers will swell due to the water. You can use a special fiberglass oil filter element.
The other problem with water in the system is it will freeze when you cross a throttling device and drop below 32 dF (0 dC).
I have designed systems fro hydrocarbons both with and without filter drier cores. Some were full flow driers and others were bypass type.
If the system is properly evacuated and dehydrated, water will not be a problem. However, if you introduce some water into the system due to poor maintenance procedures, you can have problems.
Ken
-
13-02-2007, 09:13 AM #43
Re: Propylene System
I don't know who can provide the suitble filter drier,solenoid valve,thermostatic Expansion Valve.which company can do?
-
14-02-2007, 02:50 AM #44
Re: Propylene System
For a filter drier I have used Sporlan (with steel pipe connections). I do not recommend using a Thermal expansion valve on hydrocarbons. If you must, go with Sporlan and get them to make a selection. As for solenoids, you will need to get one that is a Class 1, Group C and D, Division 2 area classification. Try Parker (Refrigerating Specialities) or Asco. I know they can meet the US explosion proof requirements, not sure about PRC.
I hae only worked with one or two DX hydrocarbon systems, as most use a flooded design evaporator. If you go DX, set your TXV super heat for 18 to 20 dF superheat. I also like ot use a suction/liquid heat exchanger to insure the suction is dry. A little hydrocarbon liquid will really mess up a compressor in short order. If your compressor is a recip, plan to rn with the crankcase heaters on full time to keep the oil warm and the hydrocarbon driven out. Probably ahve to do the same with a screw compressor. Hydrocarbon refrigerants do not superheat a lot when compresed, so you really need t watch the oil. You will have to run a poly-glycol based lube oil as recommended by the compressor manufacturer.
Good luck.
Ken
-
14-02-2007, 04:33 AM #45
Re: Propylene System
From what I remember propylene (R-1270) has very high dilution rates with oil, so it is very important to keep the oil warm enough. (which is what TXiceman is saying)
If the crankcase (for a recip) or the oil separator (for a screw) pressure and temperature relationship are known, you can look at the dilution curves to see the impact on the amount of dilution to maintain the minimum required oil viscosity (by the compressor manufacturer).
Don't be surprised to see a high viscosity oil recommended. By the time the oil and refrigerant have stablized, the oil will have thinned out to a much lower viscosity.
Hydrocarbon systems are not very forgiving of mistakes.
-
15-02-2007, 01:18 AM #46
Re: Propylene System
I am confused.Those company you all stated, parker,spoland,danfoss etc,have still not replied me whether they can do. I wanna use the TXv ,drier filter,solenoid to the economic exchanger(for screw compressor).But Danfoss dont recommended in hydrocarbon system,parker have not reply clearly.I.....
-
15-02-2007, 03:38 AM #47
Re: Propylene System
It is sad to note that Sporlan has lost most of it's expertise in using TXV's on hydrocarbon refrigerants. If I remember correctly, is does require a special bulb charge...but I don't remember the charge.
For Solenoids and pressure regulators, you night try Hansen.
Since this is on a screw compressor, what is the capacity and temperature? I did not spot it in the past post on this thread.
With a DX design, you need to be very concerned with proper tube velocities and possible multiple circuiting to insure oil return to the compressor.
The synthetic oils used with hydrocarbons do dilute and are very viscous at lower temperatures. You do need to look into the dilution. Best oils for these applications come from CPI Engineering in the USA.
Ken
-
16-02-2007, 03:22 AM #48
Re: Propylene System
Thank you TXiceman.
Things seem badly to me.'Cause all the parts for the R1270 system are difficult to select.TXV,Solenoid,Drier filter.....Danfoss,Parker(spolan is a subcompany to Parker),Hansen cant provide suitble parts for R1270.I am just looking for another way .
The system is a large one. Capacity is Te=-32C,Qe=4000kw;Te=-15C,Qe=2184kw.I have selected 2 sets unit with volume 7240 m3/h for first case,1 set unit with volume 4700m3/h.
You are right, I use the CPI synthetic oil.Now CPI haven't decided which type oil better.CP4600-68 or CP1507-100?waiting for the decision from CPI.
With a DX design, you need to be very concerned with proper tube velocities and possible multiple circuiting to insure oil return to the compressor.
sagittarius
-
16-02-2007, 04:07 PM #49
Re: Propylene System
Originally Posted by sagittarius
How many evaporators do you have on this system and what are the capacities of each?
Since you are using a hydrocarbon refrigerant, the electrical devices will have to be rated for explosion proof atmospheres. Hansen may not allow the use of their components in this duty if they are aware of the area classification.
On a system this large you may have to use multiple liquid line driers to acheive a suitable capacity...If all else fails, ask for help.
-
18-02-2007, 02:30 AM #50
Re: Propylene System
4000KW is too large for DX control unless you have severla smaller evaps and I don't like to use D control this low in temperature.
You really need to be looking at a conventional flooded design and oil stills to get the oil back.
Ken
Similar Threads
-
Daikin fault codes
By Chris2005 in forum Air ConditioningReplies: 45Last Post: 21-03-2012, 10:09 PM -
System Burn Out Troubleshooting
By altaf22m in forum Technical DiscussionsReplies: 13Last Post: 07-05-2010, 09:24 AM -
Burn out System, Clean up procedure. & Troubleshooting.
By altaf22m in forum CommercialReplies: 19Last Post: 15-04-2008, 07:03 PM -
Refrigeration system proposal; comments please.
By DaBit in forum Technical SpeculationsReplies: 13Last Post: 01-01-2003, 03:42 PM -
Automotive A/C Vent Temp Range vs System
By Don Browney in forum Air ConditioningReplies: 1Last Post: 15-05-2002, 06:19 AM