Thread: VRF Pipework Design
-
09-05-2024, 09:22 AM #1
VRF Pipework Design
Morning all,
Hopefully the correct section.
I am not 100% on VRF systems and pipe design so hoping someone may be able to assist. I have a piping and wiring diagram so pretty happy on pipe sizing.
Now, my main concern is linear thermal expansion on 1 1/8" pipe. Will be installing 65 odd meters vertically down a riser (plus the rest of the system) and have done some calcs and would be looking just shy of 100mm linear expansion possibly.
The bottom of the riser I will then break through into offices running horizontally. Need to maintain flow as best as possible, so no street bends will be installed, all long radius bends, due to longest run being 194m.
Now, would I best doing the below?
I'm leaning towards the loop but being 1 1/8" not sure I can get that, wanted expert installers opinions.
Would I need these loops on the vertical and horizontal runs?
Capture.jpg
Many thanks for the helpLast edited by Stretch79; 09-05-2024 at 09:32 AM.
-
09-05-2024, 03:51 PM #2
Re: VRF Pipework Design
Application Note 2030:
Thermal Expansion of Refrigeration
Piping In VRF Systems
Check this on http://www.mylinkdrive.com
-
09-05-2024, 04:17 PM #3
Re: VRF Pipework Design
Hi there, the link won't open
-
09-05-2024, 09:16 PM #4
Re: VRF Pipework Design
Is it 3 or 2 pipe VRF?
Is this the suction pipe?
If 3 pipe then the suction will remain suction, where would linear expansion come into it? ( am open to new knowledge btw, this isn't something i'v'e come across except on discharge lines?)Mostly found in the southern part of this green and pleasant land.
-
10-05-2024, 06:17 PM #5
Re: VRF Pipework Design
-
15-05-2024, 04:16 PM #6
-
17-05-2024, 05:57 PM #7
Re: VRF Pipework Design
No bother Stretch, i was scratching my head myself over it as well