Results 1 to 3 of 3
Thread: Carel EVD ICE
  1. #1
    Join Date
    Feb 2024
    Location
    Belgium
    Posts
    3
    Rep Power
    0
    Carel EVD ICE
    Hello,
    EVD ICE display 9. Utracella display alarm ELE. Ultracella output comp and Fans.
    I cannot find in the manual what the number 9 means.
    The valve stays closed.
    After reset (power off) everything worked back fine.
    Anybody knows this?
    Greetings Fernando
  2. #2
    Join Date
    Oct 2001
    Location
    Nottingham UK
    Posts
    5,667
    Rep Power
    51
    Re: Carel EVD ICE
    From the user manual, the only reference to a number 9 display is in the gas table.
    9 means gas type R600a
    https://www.google.com/url?sa=t&sour...q2os8Pohqhr0c-
  3. #3
    Join Date
    Feb 2024
    Location
    Belgium
    Posts
    3
    Rep Power
    0
    Re: Carel EVD ICE
    Yes, i saw that. But it was programmed R744. It does not change himself, i guess.
    I ordered a new one for be sure.