    Pipe Sizing on Multiple Evaporators
    Hi Guys - New member, please go easy on me
    I'm doing something a little bit different; I've installed similar systems, but now working for a new employer have been asked to both design and install.
    So it's going to be a 150kw cold room; setup will be 2x 75kw systems with 5x 15kw evaporators for each unit. 5C room temp, 10k superheat, TEV & magnetic valve (each with its own controller) on each evaporator & inverter controlled condensing units to control the required load. Total Piperun 35m, and will have an 8m lift (condenser will be lower)
    I have a rough idea based on my training and literature online to judge I need 2.1/8" Suction & 7/8" Liquid, and is also the connection coming off the condensers (coincidental), but how do I determine the pipe sizes that lead to each/ evaporator?
    So, I'm expecting to use 15kw for my calculation, which gives me 3/4" & 1/2" pipework. Does this sound about right?
    Any help is much appreciated
  2. #2
    Join Date
    Jun 2017
    Location
    Norway
    Posts
    32
    Rep Power
    0
    Re: Pipe Sizing on Multiple Evaporators
    Download Danfoss coolselector, it will size the pipes for you
  3. #3
    Join Date
    Sep 2021
    Location
    UK
    Posts
    2
    Rep Power
    0
    Quote Originally Posted by HwT View Post
    Great tool - doesn't seem to allow for multiple evaporators though, so whilst it is of help, doesn't provide the full picture
  4. #4
    Join Date
    May 2012
    Location
    England
    Age
    60
    Posts
    1,528
    Rep Power
    37
    Quote Originally Posted by Fishtank View Post
    What size are the evaporator pipe sizes?
    Also make sure you plan for oil traps and oil return.
    Rob
  5. #5
    Join Date
    Jan 2006
    Location
    Norway
    Posts
    1,043
    Blog Entries
    4
    Rep Power
    31
    answered wrong question
    Mod feel free to delete this
    -Cheers-
    Tycho
  6. #6
    Join Date
    Oct 2021
    Location
    London
    Posts
    1
    Rep Power
    0
    I agree with this question
    Needs clarification
Posting Permissions
  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts