    Apr 2021
    uk
    5
    Mitsubishi MUZ-GE25va(charge question)
    Hi all
    Just fitted a split unit as above,looking at the refrigerant charge chart.It gives the quantity for pipe length one way only.Are they already taking into account its x2,or do i have to x2.
    Here's the link to the chart :-
    https://www.manualslib.com/manual/11...page=20#manual
    A previous Mitsubishi unit i fitted it just gave a simple per metre measurement.
    Thanks all
    Matt
    5,667
    Re: Mitsubishi MUZ-GE25va(charge question)
    Unit is charged for 7m.
    Additional charge is 30g/m for any length over 7m. So for a 10m indoor/outdoor pipe length you would add 3 x 30g.
    Additional charge is only measured on the liquid line.
    This unit is also giving a simple per metre measurement.
    Although this unit uses the entire pipework and indoor unit as the evaporator the suction pipe should be almost 100% vapour.
    The discharge line to the indoor unit is is after the unit expansion device so could be considered to be in a mixed state. Therefore you only need to add refrigerant to maintain the required state in the discharge line.
    Apr 2021
    uk
    5
    Thanks for the clarification chaps.
    Apr 2021
    uk
    5
    Hi again
    I'm fitting a toshiba unit now in the lounge ,its an rav-sm800,does the same apply,
    this is the charge table http://www.toshiba-aircon.co.uk/asse...sion_11_5c.pdf
    .so would be 40g/m one way,{i don't include the return,as it were}
    in the installation it says total pipe length
    https://www.manualslib.com/manual/92...?page=3#manual
    Apr 2008
    Southampton, England
    49
    1,024
    It'll be the same as before, one way only.