    Mar 2021
    Belize
    1
    York Chiller YCIV Suction Pressure Limiting
    Hi Guys
    Please see below data if anything seems abnormal:
    System running at 100%
    PRESSURES
    Suction = 26 Oil = 177 PSIG
    Discharge = 192 PSIG
    TEMPERATURES
    OIL = 123.4
    SUCTION = 43.5 F
    DISCHARGE = 159.4 F
    SUCTION
    TEMP = 43.9
    SUPERHEAT = 13.2 F
    SAT TEMP = 30.7 F
    DISCHARGE
    TEMP = 159.5 F
    SUPERHEAT = 32.2 F
    SAT TEMP = 127.3 F
    MOTOR TEMPS
    T1 = 120.5 F
    T2 = 134.6
    T3 = 95.6 F
    FLASH TANK
    LEVEL 29.4
    FEED VALVE PERCENT OPEN = 46.4
    SUCTION SUPERHEAT = 15.1
    DRAIN VALVE OPEN = 54.7
    CHILLER WILL SOMETIMES JUST SHUTDOWN AND NOT GIVE ANY ERRORS..WHAT AM i MISSING GUYS
    Jul 2007
    LIbya
    58
    72
    Re: York Chiller YCIV Suction Pressure Limiting
    pleas what is the application that this chiller is intended for?
    3,363
    Discharge pressure looks high!