    Aug 2017
    Deutschland
    1
    Carrier Vector 1800 turns off AL41
    Hello
    I have a problem with a Carrier Vector 1800.
    At outside temperatures above 30 ° C , the engine will run for 15 minutes, then the engine will be out of AL 41.
    Just before she turns off the high pressure rises above 25 bar.
    Capacitor was cleaned.
    Thank you
    Feb 2016
    Germany
    33
    2
    Re: Carrier Vector 1800 turns off AL41
    Hello,
    you should update the microprocessor Software to the newest (05.16.00).
    When its done, you have more options to activate.
    In the Configuration Menu, you have the Menu AC Power Settings.
    Now you have to activate "High Amb Diesel Offset"
    Dec 2010
    devon
    837
    Fit your gauges and just check that pressure is being reached I had one do that because the truck pulling it had eminox exhaust stacks and it filled the coils up with soot good wash out of it went good as new unit
    70
    4,703
    47
    Nice to read your knowledgeable input Charlie.