    Oct 2008
    newbury
    1,444
    Hitachi RAK splits
    chaps
    full model RAK 18NH5
    Around 10 years, twin split , outdoor won't run but not throwing up a code?
    Apr 2008
    Southampton, England
    49
    1,023
    Re: Hitachi RAK splits
    Temperature probe out of calibration somewhere?
    Oct 2008
    newbury
    1,444
    Quote Originally Posted by Tayters View Post
    twin so would expect one to run? both indoor fans operate and no flashing lights..
    Apr 2008
    49
    1,023
    Ah, was thinking more the outdoor unit.
    The VRF's need the compressor probe on top to be over 40°C I think it is before they run, not sure on the multi set up though.
    ireland
    1,451
    As per Tayters, Might be no harm to check the sensor on compressor, if it's faulty then no run, no fault shows either if i remember.
    Oct 2008
    newbury
    1,444
    ok I'll check.. bit poor show for them not to integrate a sensor fault in the fault circuit..
    Feb 2005
    United Kingdom
    56
    Flashing lights on outdoor PCB. 7 times is abnormal thermistor on those models