Refrigerant Recovery R404a
Hi guys, I'm a new member so please be easy on me.
I'm new to the industry and looking for some information.
I have a blast freezer bitzer compressor to change out, I'm thinking all I need to do is shut the service valves and recover the vapour inside. Now all i have worked on is recovering R404a in a liquid state, no problem. But now I'm recovering in a vapour state, do I turn the recovery machine on vapour setting and connect my hoses to the liquid valve still on the recovery bottle? (Or vapour) as I'm guessing I want the refrigerant to go into the bottle in a liquid state?
Sorry if this is a stupid question, but I would really like to know the correct method
Thanks in advance
-
10-09-2016, 01:29 AM #2
Re: Refrigerant Recovery R404a
.
It does'nt matter too much which valve you put it into the cylinder.
I alway put it in through the liquid port because I always draw liquid
out and it saves messing round with the bottle adapters and such.
As for your machine if it has both a liquid and a vapour setting, then yes
pull it out in the vapour and push it into the cylinder through any port,
like I said I always use the liquid side of the cylinder anyway.
Regards
Rob
... ... -. .----. - / -- --- .-. ... . / -.-. --- -.. . / --. --- --- -..
-
10-09-2016, 01:53 AM #3
Re: Refrigerant Recovery R404a
Hi Rob,
Appreciate the quick reply and info.
One more question, does the recovery unit act as a condenser to change it from a vapour state to a liquid state?
Cheers
-
10-09-2016, 03:43 AM #4
Re: Refrigerant Recovery R404a
Hi everyone,
I m sorry i can not find own to create my own post... (it s the first time I use a forum in my all life...)
anyway,
I want to buy an ice cream machine to do some street ice cream but apparently the gas is R404A and I will use the machine outside with a temperature around 50degres... I saw than it could be dangerous to use the R404A in that temperature condition... and I don t want to risk to have any trouble or play with a potential bomb......
could you please let me know what could be the gas able to hit -40/-45 degrees and able to run with a environmental temperature around 50 degrees?
thx in advance for your understanding.
-
10-09-2016, 04:19 PM #5
-
10-09-2016, 05:05 PM #6
Re: Refrigerant Recovery R404a
Another trick, if you are recovering any vast amounts of vapour, is to cool the recovery cylinder whilst you are reclaiming. Normally we do this by having a trickle of water on to the cylinder ensuring it is wet and acting as an evaporative cooler, otherwise as you push the hot vapour/liquid in to the cylinder it will get warm and this will slow down your recovery progress.
-
10-09-2016, 05:16 PM #7
Re: Refrigerant Recovery R404a
Nice one, thanks for the information guys you've cleared that up for me!
You learn something new everyday
Cheers
-
10-09-2016, 06:43 PM #8
Re: Refrigerant Recovery R404a
If you are just seeking to empty the compressor of refrigerant to enable replacement, recover the refrigerant into the receiver, no need for a recovery cylinder then.
Mostly found in Oxfordshire, UK :)
-
10-09-2016, 07:37 PM #9
Re: Refrigerant Recovery R404a
Also got to change out the single PRV's on the water cooled condenser to duel PRV's. It's has a standby unit with a common receiver so need to keep the other system running while changing this out.
When going to charge back into the system, do you use the recovery unit to pump the liquid back in once the pressure has equalised from the recovery cylinder?
-
10-09-2016, 11:01 PM #10
Re: Refrigerant Recovery R404a
Yeah, pump it back in with the reco machine.
Mostly found in Oxfordshire, UK :)
-
11-09-2016, 02:00 AM #11
Re: Refrigerant Recovery R404a
Why not just use a well vacced out recovery cylinder,shut off the service valves and let the vapour transfer to the cylinder?
-
11-09-2016, 10:23 AM #12
Re: Refrigerant Recovery R404a
I thought R400 series refrigerant had to be recovered/charged in liquid form?
-
11-09-2016, 10:53 AM #13
- Join Date
- Sep 2007
- Location
- Split Croatia
- Age
- 57
- Posts
- 6,151
- Blog Entries
- 6
- Rep Power
- 36
Re: Refrigerant Recovery R404a
Charged as liquid and recovered in any state, as long as you ensuring that all recovered refrigerant will be returned to system.
Reason is fractionation. If you recover and recharge all refrigerant then there is no fractionation no matter of liquid or gas state of refrigerant.Last edited by nike123; 11-09-2016 at 11:13 AM.
-
11-09-2016, 02:56 PM #14
Re: Refrigerant Recovery R404a
Thanks for that, I understand now how recovery and charging works now.
It's much appreciated all your help
Cheers guys
-
16-09-2016, 08:09 AM #15
-
20-09-2016, 11:23 AM #16
-
21-09-2016, 08:59 AM #17
Re: Refrigerant Recovery R404a
Sure, problem comes with big setups/large gas quantity