28-05-2004, 09:10 AM #1
fluorecent tubes in fridge/freezers
hi all,
can anyone tell me if there is a special type of fluro tube required for a fridges and freezers? do regulars ones ignite okay under these temps? if not, what is the type of tube i need?
28-05-2004, 11:31 AM #2
Re: fluorecent tubes in fridge/freezers
hi slothslag,
in cold stores down to 0C there should not be any problems with fluorescent lamps ie all components are ok.
in freezers if you insist of using fluorescent light, you need special electronic starters.
why not use regular 240 bulbs in a water sealed housing ano starting problems.
chemi
28-05-2004, 11:35 AM #3
here is a link to danfoss electronic ballasts
chemi
http://www.danfoss.com/journal/2_00/Bagside.htm
28-08-2005, 05:08 PM #4
Yes electronic starters. Green starters. But make sure the defusser is sealed correctly.
:eek:
28-08-2005, 08:01 PM #5
Even with electronic starters, ignition is not the problem but it takes quit some time before the lamp reaches it's full lighting capacity (5 minutes at least)
So if you switch off the lights each time you leave the freezer, then you should better install regular lamps like Chemi said.
We allways install regular lamps, unless they are kept on the whole day.It's better to keep your mouth shut and give the impression that you're stupid than to open it and remove all doubt.
28-08-2005, 11:29 PM #6
slothslag
you need 100 watt rough service lamps these last longer in the sealed units far better than fluorescent lights
maddfridge
24-11-2005, 08:54 AM #7
Originally Posted by Jus Walker
other wise you will find that it will produce ice inside the diffuser, when the temp rises this will melt causing
spoilage inside the case.
A bit of thumb gum in the bores at either end of the tube
should be fine
cut your diffuser , fit , but do not seal around it.
you will need an electronic ballast
this should do away with the starter.
we fit standard tubes to our cases , yes it takes 5 minutes for them to reach full illumination, but they are brilliant, these are fitted to freezers that have a set point of -25 degrees celcius.
Hope this helps !Last edited by fridg; 24-11-2005 at 08:59 AM.
The primary function of the design engineer is to make things difficult for the fabricator and impossible for the serviceman.
24-11-2005, 12:49 PM #8
Here we use GE CWHO (High Output) 6 footed tube, bright & lasting for walk-in chillers.
capillary tubes
By JimmyMurphy in forum FundamentalsReplies: 2Last Post: 24-06-2006, 07:49 AM -
Heat transfer through tubes
By Peter_1 in forum FundamentalsReplies: 3Last Post: 27-03-2005, 09:39 PM -
Obstructed Capillary Tubes
By terrygoodrich in forum Trouble ShootingReplies: 9Last Post: 17-03-2005, 02:48 PM -
reduce thickness of bended copper tubes
By rlim in forum Air ConditioningReplies: 4Last Post: 08-07-2003, 10:58 PM -
capillary tubes and mass flow when fed with liquid/gas
By DaBit in forum FundamentalsReplies: 15Last Post: 24-10-2002, 06:52 PM