03-10-2013, 07:20 PM #501
Re: all reefer container problems/daikin/carrier/thermoking/mitsubishi
Hello reefermechanic,
I am new on this forum and new in refrigeration jobs.I need a help about how to log in "TransCentral" section of www.container.carrier.com and download all softwares versions for ThinLine,EliteLine and PrimeLine controllers.Thank you in advance
-
15-10-2013, 12:41 PM #502
Re: all reefer container problems/daikin/carrier/thermoking/mitsubishi
[QUOTE=Ahmad Osman;285415]Peace,
I have a case of 1 unit 40ft Reefer Container (with Daikin System) shipped with consignment of vegetables with setting temperature at 0 Deg C, however, at sometime transit, noted several alarms/code D type and there on supply temperature went up between 10 to 16 Deg C (From Data Logger). What caused malfuctioned ? Also noted, 2 drain plugs, one at front end and one at door end not inserted. Please help ![/QUOTE]
good day,
for this unit daikin there are two sensor supply but that not possible to change if this unit is full.
not:but those alarms are not afect cargo,if you went to change those sensors you mast to decharge the cargo from container.
best regards
-
16-10-2013, 02:26 AM #503
-
23-10-2013, 09:17 PM #504
Re: all reefer container problems/daikin/carrier/thermoking/mitsubishi
Thank you reefermechanic for response.
I have one more question for all forum's members.-Does somebody have an user guide (step by step) how to configure controller's software versions for Carrier reefer containers. Or,give me please link to download it.
Thank you
-
31-10-2013, 08:45 PM #505
-
11-11-2013, 08:12 AM #506
Re: all reefer container problems/daikin/carrier/thermoking/mitsubishi
Hi ,
I have one of daikin lxe10e-15a problem of frequently defrost 2 hours per time.Defrost setting is 99 hr at frozen mode . before in range , again defrosting. What is problem?
Thanks
-
13-11-2013, 10:13 PM #507
Re: all reefer container problems/daikin/carrier/thermoking/mitsubishi
Hi reefermechanic,unfortunately I have no internet access all the time,because I am currently onboard.I have operation manuals of all reefers,but I need service manuals and additional service tutorials about Carrier troubleshooting.Anyway,if you are willing to help and send some useful information you can do it on: pesicgordan@yahoo.com
It will be appreciated so much.Thank you,have a nice day
-
15-11-2013, 02:09 PM #508
-
27-11-2013, 08:34 AM #509
Re: all reefer container problems/daikin/carrier/thermoking/mitsubishi
Hi reefermechanic, i want to ask about code alarm F3 @ cabin controller thermo king KV-300 II MAX
Thanks before
-
19-12-2013, 01:20 AM #510
Re: all reefer container problems/daikin/carrier/thermoking/mitsubishi
Hi reefermechanic
i want to know if you have a software or something for the diagnostics of Thermoking Sb210, 230 and 330. Im looking for service and repair manual of thèses units. I have like 20 of thoses units and we are starting to do the repair and maintenance on them but im not able to find information. Can you help me
Thank you. My e-mail is daniel.racanelli@Hotmail.com
-
29-12-2013, 12:48 AM #511
Re: all reefer container problems/daikin/carrier/thermoking/mitsubishi
Hi reefermechainc
I have one of thermoking MD 200 used Driver Operation-TS Series Truck Unit problem of frequently defrost.What problem?
Thank before.
-
29-12-2013, 01:03 AM #512
Re: all reefer container problems/daikin/carrier/thermoking/mitsubishi
I'm using Thermoking MD 200 with Driver Operation TS Series Truck Unit, it is meeting a problem of defrosting frequently .
What's problem ? Could you please let me know ?
My email : nguyenmockhiem2@yahoo.com.vn
Thank in advance !
Best regards,
Khiem
-
26-01-2014, 10:15 AM #513
Re: all reefer container problems/daikin/carrier/thermoking/mitsubishi
Hi there!
I have a Carrier 69NT40-511-12 problem. When starting up the HP side immediately shoots up to about 2300 kpa. The compressor then cuts out and short cycles like this until it overheats. I weighed in a new charge as on the nameplate but the problem persists.
When I close the suction service valve almost completely the unit runs for a few minutes until the high pressure rises too high again.
I noticed the suction pressure seems too high if the valve is backseated about 200kpa. Also the liquid level in the receiver drops very quickly upon startup
I have no experience dealing with Suction modulating vale and suction solenoid valve. Are these causing the problem?
Thanks in advance
-
05-02-2014, 08:03 PM #514
Re: all reefer container problems/daikin/carrier/thermoking/mitsubishi
Hi , help me please to find marine reefers communication software.
Daikin Container Communication System (DCCS for DECOS III G)
-
05-02-2014, 08:41 PM #515
-
05-02-2014, 08:59 PM #516
Re: all reefer container problems/daikin/carrier/thermoking/mitsubishi
Mr. Reefer mechanic help me. Give me please manual for daikin LXE10E 149g ;( this is my email address refmaster@ukr.net
-
05-02-2014, 09:08 PM #517
-
05-02-2014, 09:12 PM #518
Re: all reefer container problems/daikin/carrier/thermoking/mitsubishi
I have a problem with removing files from the refrigerated container Daikin LXE10E 149g controllerDECOS IIIG
I have a program DCCS ver.8.00 ,but it with this controller does not work.Сan you have a newer version?
many thanks.
-
06-02-2014, 10:23 PM #519
Thermoking Magnum Plus 203 service manual
Hi reefer mechanic, I recently joined on-board a container ship. We usually loaded Thermoking reefer containers especially the MAGNUM Plus 203 series and Carrier 69NT40 series. Could you please send me a copy of its service manual? My email is: johnel.aguasa@gmail.com.
Also, could you please advice me on how to clear the datalogger alarm dAL81 of 69NT40 carrier unit?
Thanks in advance.
-
20-02-2014, 07:07 PM #520
Re: Thermoking Magnum Plus 203 service manual
Welcome
I have one question. I have a TK TS200 and Thermoguard read bat = 10.6V on the generator is 13.6V. After 10-15min, the unit turns off and the display ALR 25
Where could be the cause?
Thanks in advance
-
02-03-2014, 04:38 PM #521
Re: all reefer container problems/daikin/carrier/thermoking/mitsubishi
Hi reefermachanic , can you please help me with a service manual and diagrams for a Thermoking V250 ? My email is AR74Hog@yahoo.com
Thanks so much !!!
-
12-04-2014, 01:00 PM #522
Re: all reefer container problems/daikin/carrier/thermoking/mitsubishi
I need help with my mitsubishi tu73d. I need an english service manual and english electrical diagram.
-
12-04-2014, 01:01 PM #523
Re: all reefer container problems/daikin/carrier/thermoking/mitsubishi
Please send me a private messsge if you csn help. I cant understand the controls of the systemcoz its in japanese
-
13-04-2014, 10:29 PM #524
Re: all reefer container problems/daikin/carrier/thermoking/mitsubishi
Hi reefermechanic,
I'm in the haulage business,my co. recently decided to try our hands on refrigerated transport so we purchased a Thermoking V500 max tc 20 mounted on a mercedes benz atego truck from England.
TK unit was supposedly working when purchased, but when we took delivery of the truck we discovered that the printed circuit board was missing from the unit.
We have ordered for a new PCB and we have mounted it with all required relays and fuses.
The problem now is that the in-cab control box comes on,displays the return temprature and the set.point temperature, but the unit does not come on,the fans do not work and there is no indication that the unit is working at all, even though the cooling indicator light is on.
We are still trying to run it in vehicle mode.
It is a 24v unit.
We have also tried in vain to locate fuse F21 which supposedly supplies power to the unit from the vehicle battery.
Please do you have any ideas how we can get the unit running? or any ideas what may be the problem.
Thanks a lot.
-
16-04-2014, 08:04 AM #525
Re: all reefer container problems/daikin/carrier/thermoking/mitsubishi
Hi Guys,
Pls ask the questions to me about refrigerated container units.
All the best,
See you
Reefermechanic
-
25-04-2014, 02:24 AM #526
Re: all reefer container problems/daikin/carrier/thermoking/mitsubishi
Hi Reefer Mechanic,
Would you please help me to download a operation manual for CD TTT M5, please send to:
passionplayer@live.com
best regards
Thanks a lot!
-
06-05-2014, 08:03 AM #527
-
27-05-2014, 09:52 AM #528
Re: all reefer container problems/daikin/carrier/thermoking/mitsubishi
I have a problem with a Daikin Reefer reciprocating semi hermetic compressor that was pull out some time ago. The 9 terminals on the compressor have no leads and were not marked. I need to run this compressor but do not have the wiring diagram. The model no.2HC5BLB-L and was for a Daikin Reefer container manufactured in the 1970's. Could someone show me how to wire up this compressor that as I have mentioned has 9 terminals. I am completely lost.
-
27-05-2014, 02:31 PM #529
-
28-05-2014, 12:32 PM #530
Re: all reefer container problems/daikin/carrier/thermoking/mitsubishi
Reefermechanic, Friend of mine at another FOB is having trouble with...
It's a 69NT40-541-302 running 1 or maybe 2 degrees of differential on supply/return. Won't cool below 45F here in the high desert. It got a new Controller, "Micro-Link P/N 12-00579-00 or approved equal" before I saw it and fired it up. Ran okay--Except for Alarm 67--but we don't control humidity anyhow, so I ignored it. It ran good for a few months, then cooling petered out.
Checked the usual--cleaned both evap and cond coils, fans run hard, changed filter drier and put in correct 8.75 pound charge of 134a. It pulls 8-9 amps per leg and suction of zero to -10 inches. Discharge runs 110 to 195 as condenser fan cuts in and out. So what red flag am I missing here?
-
30-05-2014, 10:34 AM #531
Re: all reefer container problems/daikin/carrier/thermoking/mitsubishi
Thanks for a response, the name plate does fade abit.
Anyway does 2HC58LD-R has 9 terminals? It looks like a dual voltage 200volts 3 phase and 440 volts 3 phase.
How do I know which terminals is for 440 volts and which terminals are for 200 volts. A wiring diagram would help a great deal. Hoping for your reply.
Johnson
-
31-05-2014, 07:27 PM #532
Re: all reefer container problems/daikin/carrier/thermoking/mitsubishi
I have 4 years experience in commercial a/c. I've currently put in for a job as a reefer tech. Is there any basic stuff that would help me out on these reefer units that's different from commercial air? Common problems, and such. Anything will be grately appreciated.
-
01-06-2014, 08:18 AM #533
-
01-06-2014, 08:28 AM #534
-
01-06-2014, 08:30 AM #535
-
05-06-2014, 05:55 PM #536
Re: all reefer container problems/daikin/carrier/thermoking/mitsubishi
Hi reefer mechanic,
I want to know about Dakin and thermo king reefer alarm online checking Web site or mobile applications ? If u have about this , help me share please? Hope for ur reply soon . Thanks
-
06-06-2014, 01:56 PM #537
Re: all reefer container problems/daikin/carrier/thermoking/mitsubishi
Hi Thein,There is no any wesite or mobile application for your request. See youReefermechanic
-
07-06-2014, 09:28 AM #538
-
07-06-2014, 09:41 PM #539
-
09-06-2014, 03:31 PM #540
Re: all reefer container problems/daikin/carrier/thermoking/mitsubishi
I am having code 26 and 32 on a sb 200 thermo king any suggestions?
-
07-07-2014, 07:24 AM #541
Re: all reefer container problems/daikin/carrier/thermoking/mitsubishi
Hi All,
I am new in this forum. can anybody suggest me how to reset AL22 on 69NT20/40? My understanding is Alarm 22 responds to the evaporator motor internal protectors.
Regards
Mohsin
-
18-07-2014, 07:47 PM #542
Re: all reefer container problems/daikin/carrier/thermoking/mitsubishi
The better question to ask is, Are the evaporator motors running? AL22 responds to loss of control voltage at TP5 on the controller (ECJ2 on the input plug). Loss of control voltage at this point stops the evaporator fans ans sets AL22. Verify which motor has failed and change it and then use the Alarm key on the keypad scroll to Clear and press enter. Until the evaporator motors are repaired the alarm will continue to appear.
-
18-07-2014, 07:55 PM #543
Re: all reefer container problems/daikin/carrier/thermoking/mitsubishi
For Carrier Alarm mobile web access go to http://www.container.Carrier.com. Mobile web application is on the Service & Support page. Nothing to download or install just access direct from your phone
-
18-07-2014, 08:05 PM #544
Re: all reefer container problems/daikin/carrier/thermoking/mitsubishi
Sounds like a failed discharge pressure regulator (DPRV). Mounted in the discharge line behind the compressor. If it fials to open then the unit shuts down on HP
-
15-08-2014, 09:50 PM #545
Re: all reefer container problems/daikin/carrier/thermoking/mitsubishi
Good day dear. Interested in one question that you probably know the answer. The manual says that the supra Carriers with a jumper to the serial port, you can change the configuration of the microprocessor and change meter hours in case of replacement of the microprocessor. Please tell me how to do it or a link to more information. You can mail in rostov-sl@mail.ru Sincerely Capri.
-
23-09-2014, 12:49 PM #546
-
03-10-2014, 10:55 AM #547
Re: all reefer container problems/daikin/carrier/thermoking/mitsubishi
Hi, i neeed mhi instruction manual book, may you hepl me? (mmcciiia-52cpe15-2bwiiinv 2baiiinv, 2baiiifv, 3baiiiav, a2v)
-
03-10-2014, 10:59 AM #548
Re: all reefer container problems/daikin/carrier/thermoking/mitsubishi
My email adress: nhadth07@gmail.com. Thanks.
-
05-10-2014, 02:31 AM #549
-
30-10-2014, 06:36 PM #550
Re: all reefer container problems/daikin/carrier/thermoking/mitsubishi
Similar Threads
-
Container Reefer Unit for Controlled Atmosphere (CA)
By reeferman in forum New TechnologiesReplies: 9Last Post: 26-08-2011, 09:26 AM -
MICROPROCESSOR DIAGNOSTICS/Differnces beteween TK/CTC
By REEFER-TEK in forum TransportReplies: 12Last Post: 27-03-2011, 04:12 AM -
Help cutting open 40ft reefer, we now have problems
By adrian_uk17 in forum IndustrialReplies: 50Last Post: 28-11-2010, 08:11 AM -
Reefer container
By stevec in forum CommercialReplies: 2Last Post: 25-01-2009, 05:30 PM