    Toshiba Super Multi SMi VRV addressing



    20140207_095757.jpgMorning all,

    I am working on numerous indoor Toshiba fan coil units -

    model number of the indoor fcu's - RAV264BH.

    (PLEASE SEE ATTACHED SCHEMATIC PIC TO ASSIST)

    Outdoor condenser is a MAR-F105HTM8-PE on R407c with a multi controller box also installed.

    I have a hard wired remote controller stating the below fault -

    'check' light is flashing and indoor units 01, 03, 05 are showing 14 - -

    I understand the 14 - - fault, but my question is, how do I determine which fan coil is unit 01, 03 and 05? As on the drawing the fcu's are showing as labelled 11-19?

    Is there a dip switch or yellow dial on the indoor pcb showing which indoor unit is 1, 2, 3 etc?

    Many thanks
    Last edited by Daz man; 09-02-2014 at 11:56 AM.



  2. #2
    Join Date
    Oct 2007
    Location
    manchester
    Age
    50
    Posts
    5,639
    Rep Power
    45

    Re: Toshiba Super Multi SMi VRV addressing

    isnt fault 14 an inverter fault?
    http://www.mediafire.com/view/mo43v0...20A90-9922.pdf
    http://www.mediafire.com/view/uacn7f...andbook(2).pdf
    2 manuals for ya
    stick it on test heat and it will be the ones that dont run
    Last edited by install monkey; 09-02-2014 at 12:18 PM.

  3. #3
    Join Date
    May 2008
    Location
    Newcastle under Lyme
    Posts
    112
    Rep Power
    18

    Re: Toshiba Super Multi SMi VRV addressing

    14 - - on a SMi condenser is G-TR short circuit protection!

    does anybody know what exactly the G-Tr refers to?

    Then its its a case of finding which indoors the controller is meaning 01, 03, & 05

  4. #4
    Join Date
    Oct 2007
    Location
    manchester
    Age
    50
    Posts
    5,639
    Rep Power
    45

    Re: Toshiba Super Multi SMi VRV addressing

    gate transistor

    Check code Operation cause
    1. Outdoor unit power source error
    [14] 2. Wiring error on inverter P.C. board
    G-Tr short circuit protective system 3. AC fuse disconnection
    alarm 4. Inverter compressor error
    (Gate Transistor) 5. Defective inverter P.C. board

  5. #5
    Join Date
    Jan 2011
    Location
    england
    Posts
    57
    Rep Power
    15

    Re: Toshiba Super Multi SMi VRV addressing

    Iv got one of these units with a A7 fault, suction temp exceeding 40 degrees... Looks like a valve is sticking and it's putting hot gas down the suction! Can't find the combination of the units in cooling to heating to mimic the fault

  6. #6
    Join Date
    Oct 2007
    Location
    manchester
    Age
    50
    Posts
    5,639
    Rep Power
    45

    Re: Toshiba Super Multi SMi VRV addressing

    run all indoors in test cool- check which indoor is poorly performing- then just run the 1 unit to proove the multi box is knackered
    Quote Originally Posted by bigspee View Post
    Iv got one of these units with a A7 fault, suction temp exceeding 40 degrees... Looks like a valve is sticking and it's putting hot gas down the suction! Can't find the combination of the units in cooling to heating to mimic the fault