carrier chiller
[B]we have 3 carrier air cooled chiller we cant access to alarm icone
who we can accses to this icone .this chiller has password levels
can you help me
12-12-2013, 10:49 AM #2
Re: carrier chiller
chiller model 30xa
21-12-2013, 08:31 PM #3
Re: carrier chiller
Password is 11
22-12-2013, 04:17 AM #4
Re: carrier chiller
i think there is not two digit password. try it for alarm access 2222.
22-12-2013, 08:46 AM #5
Re: carrier chiller
It depends on which type of display he has it is more likely to be 11 as he can't see the alarm menu.
22-12-2013, 08:53 AM #6
Re: carrier chiller
The default
password is 0111. Use the arrow keys to change each number
and press to accept the digit. Continue with the
remaining digits of the password. The password can only be
changed through CCN operator interface software such as
ComfortWORKS®, ComfortVIEW™ and Service Tool
22-12-2013, 08:56 AM #7
Re: carrier chiller
http://www.mediafire.com/view/7d9z59...30xa-4t(2).pdf
click on link for manual
22-12-2013, 09:08 AM #8
Re: carrier chiller
i'll never get a job at carrier! haha
FULL ACCESS PASSWORD — This configuration is used
to specify the full access password. Refer to Table 1, Setup
Menu, for additional information on passwords.
Allowable Entries: 0 through 9999
Default Value: 3333
LIMITED ACCESS PANEL — This configuration is used to
specify the limited access password.
Default Value: 2222
22-12-2013, 05:21 PM #9
Re: carrier chiller
Oh I don't know but could you afford the drop in wages IM.
22-12-2013, 10:15 PM #10
Re: carrier chiller
French made XA's are either the Touch screen type password 2222 or Pro Dialog with buttons password is 11 enter enter.
American XA using Comfortlink Touch Screen 2222.
22-12-2013, 10:41 PM #11
Re: carrier chiller
Have you tried turning it off and on again.
29-12-2013, 08:47 AM #12
Re: carrier chiller
thanks for all
i activated the password but the alarm( (control box thermostat))
stall appear
29-12-2013, 08:50 AM #13
Re: carrier chiller
sorry alarm is (electrical box thrmostat)
29-12-2013, 11:33 AM #14
Re: carrier chiller
Electrical box interlock alarm is the safety for control box temperature. Check your panel ventilation, also I have seen some same chillers the wiring is series connected to external flow switch and chilled water pump interlock. Hence, if the flow switch is fail the same alarm will be displayed.
29-12-2013, 01:41 PM #15
Re: carrier chiller
17-02-2014, 07:12 AM #16
Re: carrier chiller
alsalam alykom
thanks moideen for your last help .i have another proplem the touch screan not working and the chiller is runing .do you have spare part list for carreir chiller 30xa a or any carreir vender at our regon to make order to bay the spare parts. thank you again for your helps
17-02-2014, 12:08 PM #17
18-03-2014, 08:12 PM #18
Re: carrier chiller
Guys, I am new to this thread so pardon my mistakes. I have trane chillers (model ECGAL500) and trane air handling units to maintain but cant have access to the system because there is a password on it. Anyone knows how i can get it or reset it. Also any technical manual will be appreciated. Thanks guys!
14-05-2014, 06:32 PM #19
Re: carrier chiller
plz tell me how to switch off a single circuit through the display.