Discharge line bypass device utility ?
Hi
I checked a floor standing 4 ton LG split air conditioner unit
there was a bypass valve connecting between the compressor discharge line
and suction line
the tube connect the valve from discharge line is larger than the capillary which connect the bypass valve to the compressor suction line
these word are on the valve name plate
SP 280 psi
what its utility
-
Re: Discharge line bypass device utility ?
Sounds like it is used for capacity control. It's either regulating or opening at 280psi.
See Link: http://www.heatcraftrpd.com/res/pdfs...ty_Control.pdf (Page 8-9, Fig 2a)
Another reason for piping a line to the suction would be for over pressure protection. Its not recommended here in Canada but still seen frequently.
-
15-12-2013, 04:17 PM #3
Re: Discharge line bypass device utility ?
I took a photo for the valve from another unit
bcoz the tag on the valve of the first unit was removed
-
15-12-2013, 04:36 PM #4
Re: Discharge line bypass device utility ?
it's heat pump unit or not?
-
15-12-2013, 04:41 PM #5
Re: Discharge line bypass device utility ?
its heat pump unit
48000 btu
-
15-12-2013, 06:28 PM #6
Re: Discharge line bypass device utility ?
I had seen a similar circuit design in MHI units.
Tomorrow I can upload mhi documents.
-
04-02-2014, 07:42 PM #7
-
05-02-2014, 11:21 AM #8
Re: Discharge line bypass device utility ?
I think its like pre-error of HP. If compressor don't stop by currency/overheating with discharge->suction bypass, so let him work)))
-
07-02-2014, 11:11 AM #9
Re: Discharge line bypass device utility ?
-
07-02-2014, 02:17 PM #10
Re: Discharge line bypass device utility ?
First foto - Liquid injection and HP bypass ( after condenser to the suction)
Second foto - HP drop, bypass capillary tubes.
See that valve in old ME blocks r22