    Daikin RZQ140KCV4A



    Hi guys

    I have been having troubles with this unit going out on E3 error code. I have changed the HP switch as it was faulty. But now 1 month later the unit has been intermittently tripping out on the same code. It may run for 4 days without tripping.

    Could there be another issue? Does the pcb need to be reset?



  2. #2
    Join Date
    Jan 2008
    Location
    england
    Age
    40
    Posts
    113
    Rep Power
    18

    Re: Daikin RZQ140KCV4A

    Quote Originally Posted by rude View Post
    Hi guys

    I have been having troubles with this unit going out on E3 error code. I have changed the HP switch as it was faulty. But now 1 month later the unit has been intermittently tripping out on the same code. It may run for 4 days without tripping.

    Could there be another issue? Does the pcb need to be reset?

    E3 Is HP activated so i would suggest your HP was never faulty it was simply ditecting a high pressure fault, check usual suspects: Blocked condenser, faulty fan motors, blocked filter drier system over charged FYI H3 fault code means HP switch is faulty.
    Hope this helps

  3. #3
    Join Date
    Oct 2001
    Location
    Nottingham UK
    Posts
    5,667
    Rep Power
    51

    Re: Daikin RZQ140KCV4A

    The relays on the PCB that provide L / M / High speed can sometimes fail which causes the E3 fault.

    Senario

    Unit fires up on full speed fan, runs for 10 minutes, settles, and fan drops to Medium speed, but as the relay is U/S the fan stops while the compressor continues to run. With no coil airflow, HP trip occurs.

    Seen it many times on Daikins, especially the old R71F units.

    E3 can also be caused by a faulty Ambient sensor - the one that sticks out the back of the unit

  4. #4
    Join Date
    Jul 2009
    Location
    Australia
    Posts
    20
    Rep Power
    0

    Re: Daikin RZQ140KCV4A

    It wont be that Franky, its an inverter model with DC fan motors.

    The first thing I'd check is the High Pressure Sensor - its located on the indoor coil side of the reversing valve so reads LP in Cooling and HP in Heating. If running in Heating could bring up a HP fault.
    2500kpa = 2.3VDC roughly
    1000kpa = 1.25VDC roughly

    Most other components like EXV, RV, indoor airflow, outdoor airflow should cause - inverter to ramp down and fail on Abnormal Discharge Temperature (F3) before High Pressure (E3).

    Hope this helps mate.

  5. #5
    Join Date
    Oct 2008
    Location
    Australia
    Posts
    210
    Rep Power
    16

    Re: Daikin RZQ140KCV4A

    Thanks guys I'll check all those and monitor the unit