    Apr 2012
    Iraq
    623
    split ac indoor unit electric heater
    hi
    i got LG split air conditioner heatpump
    i opened the indoor unit cover so i saw electric heater on the evaporator
    what its utility
    for melting ice when evaporator frozen in cooling mode
    or as backup heating when defros cycle energized in heating mode
    Feb 2007
    2,473
    Re: split ac indoor unit electric heater
    You sure that is a heater and not an ionisation module?
    Apr 2012
    Iraq
    623
    im really not sure
    but if we assume its electric heater
    what its for
    manchester
    5,639
    ioniser...
    look at the nameplate for electrical load- prob around 50watt for fan motor and comms- if it was a heater then it would be of a higher output
    Oct 2008
    newbury
    1,444
    smoke removal
    Apr 2012
    Iraq
    623
    ok
    is there any wall amount heat pump contain electric heater in indoor unit or not
    manchester
    5,639
    mitsubishi mr slims about 10yr ago used to have a boost heater option
    imi hilo units had elec htr but theyre 20 yr old
    any electric heater will affect energy efficiency ratings- also a fire hazard too- burgerkings used to use york ducted units with electric reheat batteries in the duct - lots of flashy lights when a 90kw 3ph heater bank blows an element
    Apr 2012
    Iraq
    623
    ok
    what is the utility of those heaters
    manchester
    5,639
    on imi's they were for heating as reverse cycle heating in low ambients meant regular defrosting , on mitsi units they were an option to boost output -in cooling mode on any air con then the indoor shouldnt freeze up if aslong as the filters clean,setpoint is within limits and gas charge is ok
    Apr 2007
    371
    Quote Originally Posted by kefah View Post
    ok
    Answered your own question
    Sep 2013
    Cambridge
    44
    1
    It should be electric heater for winter use.